Customer wants me to mount his EV charger on the back of an external, plastic meter cabinet. The cabinet is a new plastic one at the other side of his drive from the house with a separate consumer unit inside. This would be an ideal location for ease of installation.
Is this allowed or will I...
I am due to carry out an electrical job in a third floor flat.
Incoming supply is TN-S.
Cannot locate a main earthing conductor inside the CU on the earth bar, just the individual circuits CPCs.
There are two earths clamped to the bottom of the metal CU, one disappearing down some metal...
Replaced the RCBOs with new ones and still having the same problem. Tried it at the socket (outdoor), and at the DB with the conductors disconnected. RCBO still failing for additional protection at 5X In (56ms).
Any ideas what could be causing this? Cheers
Thanks for all the replies.
It ended up being a mixture. I split the ring and had the low reading at both ends. I totally disconnected the neons and tested each leg and it was normal (>999M).
On the other side of the ring I discovered a dishwasher that was plugged in under the plinth. When...
I will be testing the secondary CU. It only has the earth from the MET attached to it (no bonding). In the MET is just the supply earth and one earth to each CU. Bonding is connected to the primary CU (which isn’t being tested). I assume it’s therefore ok to isolate both CUs, disconnect the...
Newbie testing question:
Two consumer units in same location.
Tails approximately 2 metres.
MET bar next to meter in another room.
Bonding attached to main consumer unit.
Where should I remove the earth from, consumer unit or MET? If MET, use a wander lead? My thoughts are to disconnect earth...