Search results

  1. marconi

    Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading

    For a split phase or two of three phase supply the neutral never carries a residual current of more than that of the highest line's current. Is the remark you made directed at the fact that the shared neutral conductor in the cable to the cottages is fed by two switched neutrals?
  2. marconi

    Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading

    Assuming Uo of 230V then calculated PFC is Uo/Ze = 230/0.97 = 237A not 27A, a factor 10 different. Is 27A a typo and you meant to write 237A?
  3. marconi

    Motor starter help.

    Do you still want help with this or have you fathomed it out already?
  4. marconi

    UK Can anyone tell me what is wrong/incorrect.

    If only it was just my crayons......
  5. marconi

    UK Can anyone tell me what is wrong/incorrect.

    Just spotted there is a wiring fault in the figure I copied and posted in my #34.
  6. marconi

    UK Can anyone tell me what is wrong/incorrect.

    I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location. The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short...
  7. 1703601788921.jpeg

    1703601788921.jpeg

  8. marconi

    3 phase problem after spark did 5 year safety inspection

    The Sp consumer unit is fed from the Henley block. Op - Please could you confirm whether the feed to 3P board second from left which looks discoloured is L1 or L2. Is this feed actually discoloured from overheating?
  9. marconi

    3 phase problem after spark did 5 year safety inspection

    Good morning. If the cooling system fed by the 3P db did indeed have three phase 3 wire motors, then even though the main L2 fuse ruptured the site‘s L2 conductors would remain energised because it is connected by the motor windings to L1 and L3. The voltage of L2 with respect to N will depend...
  10. marconi

    3 phase problem after spark did 5 year safety inspection

    Please tell me what loads were connected to the blue and brown c form sockets. Were they 3 phase motors or transformers connected to the brown sockets? If they were three phase were they 3 phase 3 wire ie neutral not used? Is the L1cable at the bottom of the 3 phase dis board - 2nd from left-...
  11. marconi

    Problems with off-peak circuit on Economy 7 - any help appreciated!

    Take a look at your electricity account or a recent bill and tell us the name of the tariff you are on. Are you with eon or some other company? what is the make and model number of the storage heaters? Are there any time switches for the hot water tank peak and off peak heating elements? Is...
  12. marconi

    Compressor 3hp motor DOL starter question

    Would you like me to visit? You live about 15 minutes away from me. Private Message(PM) me.
  13. marconi

    Compressor 3hp motor DOL starter question

    If an electric motor has been unused for a while and cools down to low temperature its windings can absorb moisture from the air drawn inside the motor casing. Obviously more of a problem during damp conditions like you mentioned. One should not attempt to dry the motor by running it which can...
  14. marconi

    Cycles per second meter

    I should point out that the meter connected as it is by its two terminals to a lead and 13A plug does not meet today's safety standards. Those terminals are exposed live parts. Similarly, if the meter mechanism is made of metal and its front face too then it could potentially be live. What is...
  15. marconi

    Cycles per second meter

    Try swapping the 0.25uF 350V dc capacitor for a new one such as this: Vishay BFC2 368 55224 220n 400V 368 Series Polyester Capacitor - https://www.rapidonline.com/vishay-bfc2-368-55224-220n-400v-368-series-polyester-capacitor-10-4136 (220nicoFarads is 0.22microFarads - 0.22uF).
  16. marconi

    Cycles per second meter

    Pikis- I strongly recommend you do not apply power yet especially from the mains because we need to confirm the technology of the meter in front of you and its designed operating voltage. I think the wiring diagram you showed, which is for a moving iron mechanism type meter, is not what is in...
  17. marconi

    12v motor causing noise in 240v system

    Would you be prepared to buy a double wound electrostatically screened one to one ie 240 to 240V isolation transformer of about 100VA ie twice the power of your laptop. I am honing in on some suppliers to recommend to you.
  18. marconi

    12v motor causing noise in 240v system

    Could you find out please whether and to what the earth pin of the 13Amp sockets is connected please? Does the 240V installation include residual current detection (rcd) circuit breakers? If you look at any circuit breakers in the boat the ones ones which are rcd will have a small press to test...
  19. marconi

    Could my meter be wired up wrong?

    Have I confused you or worse frightened you away? The tests I described may quickly decide your question.
  20. marconi

    12v motor causing noise in 240v system

    A nudge/bag. What is power consumption of your laptop which has the interference? And I would install the missing ferrite choke on the raymarine power leads.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top