Sorryhe should have put above in the first post so that we are on the first page not the last .
Agree just making the point of plastic entry to building, you can’t put plastic all around the metal structure, it’s all going pear shaped or even earth cable shapedIf the structure is metal and in contact with the ground than yes it is extraneous. But the next key question that needs to asked is "is it high resistance extraneous or is it low resistance extraneous? The low resistance extraneous is the concerning one. In both situations fault current can be exported and so there is a potential shock risk. However in the low resistance scenario fault current can also be imported (open PEN) and you now have the added danger of having heat damaging currents flowing in the electrical earthing infrastructure