he should have put above in the first post so that we are on the first page not the last .
Sorry
If the structure is metal and in contact with the ground than yes it is extraneous. But the next key question that needs to asked is "is it high resistance extraneous or is it low resistance extraneous? The low resistance extraneous is the concerning one. In both situations fault current can be exported and so there is a potential shock risk. However in the low resistance scenario fault current can also be imported (open PEN) and you now have the added danger of having heat damaging currents flowing in the electrical earthing infrastructure
Agree just making the point of plastic entry to building, you can’t put plastic all around the metal structure, it’s all going pear shaped or even earth cable shaped
 
To throw a random thought into the ring, there are reportedly now more open pen detection devices on the market since the advent of EV chargers.
I have no idea if it is economical to install open pen protection at the origin and whether that would mitigate the scenario discussed above sufficiently.
It might be possible to have more conventional bonding at the outbuildings then if the services are/ can be insulated.
I would doubt that any are up for the sort of current levels on this sort of a system, but it is an idea that would also reduce the risk of damage due to high voltages on phase-neutral arising from unbalanced loads, etc, during such a fault.

But I suspect that some reels of 35mm wire are a simpler, cheaper, and more reliable solution!
 

Reply to Main earth bonding protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
728
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
962
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
Replies
2
Views
2K
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock