http://www.bbc.co.uk/news/uk-england-london-32157618

There have been surges all over central London, one knocked the till out in nandos when I was getting my tea last night, I was livid!
 
The same as LV networks, via earth electrodes....

TT for MV? I mean the neutral point of the supply transformer. A high resistance or Peterson earthed neutral point will drastically limit fault current greatly reducing the incident energy at a fault. Solid grounding is something I would avoid in MV, even though the US does it like crazy because every other MV-LV transformer is wye-wye.
 
As far as i'm aware, all of the local MV/LV distribution network TX's are Dyn 11 (delta/wye). N-E Resistors would only be used where it is requirement to limit the fault current on the LV side. Earthing electrodes for MV and LV systems are generally separated at TX locations unless the Ra value of the electrode systems are of a suitably low value (under 1 ohm).


I don't consider MV/MV TX's as being particularly part of a local network distribution system, although in Central and the City of London the networks have been reinforced and evolved many times often in not exactly the best way, so it wouldn't surprise me at all that N-E resistors have been used quite extensively.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

UKMeterman

Arms
-
Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Small 11Kv cable fire London...
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
UKMeterman,
Last reply from
Knobhead,
Replies
37
Views
4,368

Advert

Back
Top