B
Bright.Spark
I just got a job to connect a 15 KW motor up. The run is 40 meters and to my calcs I could get away with 6mm armoured but that's with a volt drop of 9.6 volts! Just after a few opinions as to if I should run the 6mm or just go for a 10mm? The cable will be clipped direct. Cheers fellas.
Is this a single phase motor??? also what is it for???
Ok so working out 3 phase current is slightly different to single phase
The calc is P/(V x root3 x power factor)
which gives in your case 15000/(400 x 1.732 x 1) (assuming a power factor of unity although around 0.85 is more accurate
= 21.65A per phase. Even at 0.85PF it's only a shade over 25A.
So your cable needs to be able to carry a minimum of 25.65A under it's normal service conditions, assuming 0.85PF.
I would use 6mm SWA protected by a 32A C curve MCB.
Edit....in addition your max VD would be 5% of 400V = 20V, so your 9.6V is fine.
Its a compressor. It already has a flex coming out of it with l1 l2 l3 and an earth so all the starter is internal. I'm just gona run the cable and put an isolator up.
hi
if you do end up connecting it up make sure you check the rotation of the motor, when i first started i did a similar job to yours and when i ran the compressor it all worked great untill the fly wheel came flying off causing £100 worth of damage!...gutted. hope this is of use to you
regards
gary
hi
regards
gary
Going off the thread a little so excuse me
Now that is some sound advise for trainees and some sparks who rarely touch 3 phase jobs
It should be written into your brain as essential things a spark should remember to do
If you dont wire and connect 3 phase motors and want to be assured if you did so ,a little question for you
What would you do if it was reversed?
ive done very little motor work, but am going to give an answer and see wether im right or wrong and in return learn.
would i rotate a pair of phases? swap l1 and l2 over? would i do this at the motor, isolator or the board?
Fellas it was a nightmare today lol. Firstly the 32Amp C breaker kept tripping so I rang the manufacturer and they said I needed at type D! By this time it was 4 o'clock and I was giving up hope. Luckly a wholesaler came through and I quickly connected it up to my horror I found that the compressor was running the wrong way! I read the instructions and it said that an LED will come on if the motor is in reverse so I left the motor for 2-3 mins and the nosie wasnt better so I shut it off and rang the manufacturer where they told me the LED dont work and I should never believe screen readouts. Luckly the belts had come off the pulleys so there was no major damage but just be warned anyone connecting a compressor, if you think the rotation is wrong then stop the motor and try the other way! All sorted now thank god!
15 KW motor to connect
Electrician Talk | All Countries
Bright.Spark,
mechelec,
