Hi,

A while ago I posted about my neighbours 3-phase generator etc....

So he's being running through diesel like there's no tomorrow and been talking to a local barn who have said he can take the power from his property to supply their kiln.

He's been measuring the his average usage over the last month or so, an on average his kiln uses 12kw, so we will run a cable for a 15mw supply to side on caution.

So he wants to bury a 3-phase supply to the kiln from the barn. The barn is roughly 1000m away. I wanted to check to see if I'm calculating the cable size correctly.

15kw/400 x 1.73 = 64.9amps

So Woud that be 21.6amps Per phase?
I'm struggling to work out volt drop to determine the CSA of the cable?

Thanks
 
Hi,

A while ago I posted about my neighbours 3-phase generator etc....

So he's being running through diesel like there's no tomorrow and been talking to a local barn who have said he can take the power from his property to supply their kiln.

He's been measuring the his average usage over the last month or so, an on average his kiln uses 12kw, so we will run a cable for a 15mw supply to side on caution.

So he wants to bury a 3-phase supply to the kiln from the barn. The barn is roughly 1000m away. I wanted to check to see if I'm calculating the cable size correctly.

15kw/400 x 1.73 = 64.9amps

So Woud that be 21.6amps Per phase?
I'm struggling to work out volt drop to determine the CSA of the cable?

Thanks
No
 
But he can't be using 12kw per phase, so wouldn't that be the total split between phases?

His current kiln is supplied via a 20kw diesel generator. When I was there before Christmas I measured the current on each phase at that point of time and it was only like 7-8kw between all 3.
 
I was thinking round 16mm to handle the voltdrop. So what I wanted to check, the current requirements its asking for, I'm guessing that's 21.6amps rather than 64.9amps. As there's a massive difference between 25mm and 95mm!
 
I was thinking round 16mm to handle the voltdrop. So what I wanted to check, the current requirements its asking for, I'm guessing that's 21.6amps rather than 64.9amps. As there's a massive difference between 25mm and 95mm!
Good luck with the 16mm. Your more likely looking at around 95mm
 
I was thinking round 16mm to handle the voltdrop. So what I wanted to check, the current requirements its asking for, I'm guessing that's 21.6amps rather than 64.9amps. As there's a massive difference between 25mm and 95mm!

16mm is nowhere near big enough to handle the volt drop of a 1km cable route. Then the next problem will be how you overcome the earth loop impedance issue.
I suggest you do some calculations to size the cable correctly and then look at how you are going to protect said cable against an earth fault.

On a positive note, I do think you installing a 15MW supply (as per your original post) is a bit overkill!
 
You say you have clamped the load per phase, did you assess how the kiln and its controls work?, did you check all elements were in working condition and calling heat when you clamped?

Simply clamping on a temperature controlled kiln may not give you the max demand unless you are familiar how it exactly works.

Are the elements 400v or 230v, do they have 2 x 230 in series across 2 phase, an element down could effectively would take out 2 elements.

This is all before you even get to the cable size, as is the nature of such equipment it is crucial to find out if it is across the phases or per phase, assumption can be a costly kick in the nether regions.
 
The kiln has small electrical draw. There 400v fans which circulate the heat, the source of file is chipping a from a small hydronic shaft. When I measured it, everything was set to maximum demand, so the desired temp was set above max output so would have thought that would have been the highest demand even with the shaft in operation
 
If you are unsure then open the controls find the element connections and visually inspect the elements for links which my not come back to the controls, work out how they are connected and test them thus you have the values you need to work out the current required.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
Business Name
HomeCert Ltd

Thread Information

Title
3-phase cable calculation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
HomeCert ltd,
Last reply from
buzzlightyear,
Replies
22
Views
18,679

Advert

TrueNAS JBOD Storage Server

Back
Top