RCD RATING VS. SERVICE FUSE RATING

spud1

-
Arms
Hi chaps

A Wholesaler told me me this week that the RCDs in the new '18th' split load boards have to be rated at 100a because the 100a service fuse is only means of upstream overcurrent protection. But I was once told that service fuses, although marked as 100A on the cutout label are actually only actually 80amp?

Any thoughts guys?
 
So for example (bear with me here as I'm not sure I have grasped this nonsense fully), In a single phase domestic situation the DNO fuse is 100A, CU main switch is 100A. A dual RCD load board is installed with 80A RCCBs. One would have to keep the total rating of all downstream devices for each RCCB less than 80A unless the manufacturer agrees that diversity can be used for that group of circuits ? But the total for the CU could be up to 160A as the main switch is in theory protected from overload ?

Spot on - although all UK manufacturers have said, through BEAMA that they will not permit diversity so the 95% of the regulation is void and a pointless exercise. The IET should have consulted the manufacturers before writing the reg and then just wrote what the manufacturers state.

The other alternative would be to have 100A RCCBs installed with the 100A main switch.
 
Spot on - although all UK manufacturers have said, through BEAMA that they will not permit diversity so the 95% of the regulation is void and a pointless exercise. The IET should have consulted the manufacturers before writing the reg and then just wrote what the manufacturers state.

The other alternative would be to have 100A RCCBs installed with the 100A main switch.

So the OP's wholesaler was wrong with their assertion that all RCCBs will need to be 100A rated.

My example is how I used to arrange all my dual RCD boards anyway, but not installed any for a while now.
 
I tend to agree but the Reg does state manufacturers info must be adhered to and they say you cannot take into account diversity. Why the IET just never wrote the Reg to state this and keep it simple is beyond me.

In your case if the OCPD is 100A or less then what is installed downstream is irrelevant.
What is the Reg No of the one that states Manufacturer’s info must be adhered to?
 
So the OP's wholesaler was wrong with their assertion that all RCCBs will need to be 100A rated.

My example is how I used to arrange all my dual RCD boards anyway, but not installed any for a while now.

You are correct. I suppose the supplier is saying that we should assume 100A unless proven otherwise.
 
No, it doesn’t specify CUs, but it does make reference to the British Standard that applies to CUs and to the overall rating of the assembly, which suggests the assembly is ‘type tested’ and therefore a CU.
 
No, it doesn’t specify CUs, but it does make reference to the British Standard that applies to CUs and to the overall rating of the assembly, which suggests the assembly is ‘type tested’ and therefore a CU.

BS EN 61439 is the Standard for Low-Voltage Switchgear and Controlgear.

Anyhow, where are you going with this point?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
spud1,
Last reply from
spark 68,
Replies
50
Views
17,502

Advert

Back
Top