i'd give it a C3 for excessive Zs , no danger but requires improvement.

Should start with capital I and a comma after danger. :-)

Re OP: I've seen similar in a hotel.
In my case, the geezer I was testing with was giving old code 2s for RFCs on 2.5, on rooms with their own DB, protected by 20A breakers! Never been any reports of nuisance tripping.
 
In order to code it would have to not comply....if the disconnection time are met it complies.

problem with RCBO is not only does it have to comply with Earth fault but overcurrent as well that will bring your loop impeadence down to meet trip time on over current
 
The problems come, when the RCD covering these non compling Zs circuits fails!! And as this is a multi-storey hotel, i know what i'd be doing!! lol!!
 
problem with RCBO is not only does it have to comply with Earth fault but overcurrent as well that will bring your loop impeadence down to meet trip time on over current

Zs has nothing whatsoever to do with overcurrent,only earth fault current.
 
Room service maybe, but the mini bar would still be pretty much in tack, i'm not a big drinker!! lol!!

I was thinking more of, well and truly covering my arse on that certificate!! lo!!
 
What happens when no cpc on older lighting circuits , how do you test if this circuit will disconnect ? Do you just add up R1+Rn to ze
 
What happens when no cpc on older lighting circuits , how do you test if this circuit will disconnect ? Do you just add up R1+Rn to ze


well there is no Zs without an earth.
and a dead short between L & N will disconnect device fairly quickly without the need for any testing :-)
 
Last edited by a moderator:
in this case the rcd would disconnect (assuming it works). you would not get a fault to earth except through a body.
 
I am just going to put these Zs fails a C2 fault and recommend the mcb get downgraded to either 16/20amp, I've always been led to believe that a 30mA RCD is for additional protection on a TN arrangement, I do alot of new build house tests where the full d/b is RCD protected and it would make the Zs test pointless if I went down the line of relying on the RCD for tripping times?
 
I am just going to put these Zs fails a C2 fault and recommend the mcb get downgraded to either 16/20amp, I've always been led to believe that a 30mA RCD is for additional protection on a TN arrangement, I do alot of new build house tests where the full d/b is RCD protected and it would make the Zs test pointless if I went down the line of relying on the RCD for tripping times?

I understand what you are saying....but a new build TN system should be designed with OCPD disconnection times in mind. An EICR is only concerned with compliance with Bs 7671. IMO you would be wrong to code 2 a circuit which complies with the required disconnection times,reg 411.4.4 applies,and clearly states an RCD is a permitted device for earth fault protection.
An EICR is not about personal preferences.....good luck with claiming a circuit which complies with 411.4.4 is 'potentially dangerous'.

Edit
Just to add -you could always include a recommendation in your report that the issue is addressed,giving reasons. But a code 2 is an automatic 'unsatisfactory',potentially forcing the client to part with a wad of cash. It's going to be hard to justify your report when the client finds out he's spent a lot of hard earned on an install which actually complied with the regs.
 
Last edited by a moderator:
I agree with you on new builds, should be designed to trip in time regardless of RCD. You would still need to carry out the test though to confirm CPC is continuous.
I was replying to nicsin02 (not great at this forum thing!):
I am just going to put these Zs fails a C2 fault and recommend the mcb get downgraded to either 16/20amp, I've always been led to believe that a 30mA RCD is for additional protection on a TN arrangement, I do alot of new build house tests where the full d/b is RCD protected and it would make the Zs test pointless if I went down the line of relying on the RCD for tripping times? !):
 
Last edited:
as wiepuller said, a code C2 is a non satisfactory, potential danger, so a bit OTT. i'd go with C3, improvement recommended, and as your recommend downrate MCBs from 32A to 20A.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
failed Zs
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
nicsin02,
Last reply from
ojchurch,
Replies
31
Views
10,244

Advert

Back
Top