hi all,
i have got an oven and hob to connect to an existing supply.
the oven is 5.7kw and the hob is 6.8kw.
just been having a read up and it says that 2 items can be connected to a single cooker circuit as long as they are under 15kw
am i reading this right![]()
hi al,Not sure if you`re reading the same text as me, Flukey, but i read 50A for both!
That`d give you a theoretical max overhead of 12 KW - assuming the ratings you supplied relate to current draw @ 240v. As in, 6.8 + 5.7 / 240v = 12. Even if its @230 it`ll be max 54.3A pull.
Although you can`t be as generous as if they were Cookers proper, collectively you could still apply some demand & diversity. The hob will have integral thermo control preventing all `rings` remaining on at once. Even the hob will cycle. So i`d have no problem convincing myself as designer that the Ib could reasonably be assumed <50A
hi al,
thanks for the reply.
it does state max 50A for both, but above that it says "A 30 or 32A circuit is usually appropriate for household or similar cookers of rating up to 15kW
ive attached the page for you
hi mac,Cooker circuits rated between 16A and 50A may supply two or more cooking appliances installed in the same room. The cooker switch should be installed within 2m adjacent to the appliance(s). One cooker switch can be used to control more than one appliance.OSG Page 160
hi macI've always put any circuit over 2kw on a dedicated circuit,that is just me.I found this and it seems you can put more than 1 appliance on a cooker circuit.Can't wait till Xmas day when the whole lot is going full pelt.
electric cooker circuits
You didn't state what size the actual cable was,as quoted by electricAl in another post.16mm for 15kw cooker
hi mac
it does state the cable size as 10mm
yet to find a cooker circuit in a domestic situation run in 16mm![]()
Did one about a year ago.
12KW cooker about 20 meters.
Now THAT was fun.
hi jasonDid one about a year ago.
12KW cooker about 20 meters.
Now THAT was fun.
hi jason
so you reckon i would be best running a separate 6mm circuit for the hob then and leaving the cooker on existing circuit![]()