I've been let loose today to do a PIR, EICR, E, I,E,I, O what ever they wanna call them these days in an empty flat and have an annoying CPC broken in RFC.

  • 2 bed flat
  • 3 way CU - Cooker (30), Lights (6) and RFC(30)

End to end of r1 and rn fine but r2 is broken.

This is what I did-
  • connected opposites r1 and r2 in choc and using my kewtech R2 adapter went round testing all sockets and nothing was showing as broken.
  • removed said sockets and nothing is loose or broken and even tightened all screws to make sure.
  • connected one leg of r1 and r2 and found that only one socket in the flat was giving me a reading.
  • connected other leg of r1 and r2 and guess what! everything else but that socket above had a reading.
  • take the cover off again, everything looks right
  • do my end to end reading again, r1, rn all fine but r2 still broke.

Flat is empty no spare way make them into 2 radials if i wanted.

everything else in the flat is fine.

what am i missing????

thanks in advance.
 
An EICR you are just reporting your findings, not fault finding and fixing.
C2 and further investigation required.

Sounds to me like you have successfully identified the leg of cable that is missing it's CPC though. My money would be on a JB under the floor between the sockets.
 
Not that I'm into testing..........but from what you say using your R2 adapter you are obtaining an earth at each and every socket, am I right? If so break must be between CU and a first socket on a particular leg of the ring.
 
Are you sure you've not missed anything, like a fused connection unit, a socket hidden behind somewhere etc.? I once found the cables for a socket behind the wallpaper, an open drylining box papered over, with an open L and N connection!

When testing just one cable R1+R2 connected, if you measure carefully, you can often place the sockets in the order they are connected round the ring, though bad connections and poor switches can make this a bit hit & miss - unless you open each socket up and test at the terminals behind. Might help determining where to look.
 
Thanks for the help.

I searched that flat top to bottom, only FCU was a combi boiler spurred off the RFC but obviously disconnected it.

There were however an awful amount of nails/screws in the walls, some in the permitted zones. maybe i should of testes a screw or two LOL.

Murdoch - We are more than likely to be replacing the old CU for a new one and thought as i was already in the flat with cover off and wires in hand i might be able to prevent us/me having problems if we do get the CU change. This was my only job for the day as not needed elsewhere and wanted to test it as much as possible to gain better understanding of why and how its doing it.
 
If there is a break in CPC and you have found that the readings change at one socket remember the break could be at the next socket along
like so, either of these breaks would give the same results:
[ElectriciansForums.net] Broken CPC, done all I can but still no luck.
 
He 'a already identified that the fault is between the first and second socket, so what is there to be gained by doing other tests around the ring?

Testing the cable between those 2 sockets would be a good idea.
 
There were however an awful amount of nails/screws in the walls, some in the permitted zones. maybe i should of tested a screw or two LOL.

It could be a screw in lots of places. As an example, I once had a RFC with a CPC break, which turned out to be caused by a screw through the cable some 20 years prior when an extension had been built, the screw was to hold a moved stud wall to a joist, under a floor board. Actually the screw had shorted CPC to L, been removed (and fuse replaced (and nothing said to the owner)) and the screw inserted somewhere else nearby. The evidence was the flashover marks in the cable when removed. As to finding it - a cable tracing kit, tracing the cable round in the void between floors, with signal injected onto CPC from each end in turn.
 

Reply to Broken CPC, done all I can but still no luck. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
250
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top