I've just finished a part rewire of an estate agents shop/office, part of the spec was to give the window display guys a feed via 2 x DB sockets for their LED window display as below.

[ElectriciansForums.net] LED Window Display Problem?

Each column is on its own driver via a plug from my supply. The supply is from a 2.5mm on a Squre D C16 MCB, (SQO range btw) clipped direct and trunking (enough info for you guys :wink: )

Owner of the estate agents has just called me now saying that one column went off yesterday and that the other two went off today at different times! I told him that it will be the drivers of each unit, they have a thermal cut off switch and it must have kicked in. But the window display man (owner of the company) says it isn't!!! They have never had this problem before and it must be the electricians fault!!!!! We will see on Monday. The MCB has not tipped, all tests are great (new circuit). It must be his equipment that he has plugged in?

That is my question. How do I prove that it is his drivers at fault??? I may ask Test-Meter to loan me a thermal camera and take readings at different times of the day of the drivers.

Any help on this will be great lads, thanks in advance.


btw I will be telling the window display guy to go and multiply on Monday, should be an interesting conversation :6:
 
Under the Back wheels with jokes like that.
Only kidding Nephew
 
Badly installed lol. Worried, NOT. GMES saying I'm out of my death!!!! Knew I get a ribbing for asking this question pmsl.


It is in 3m of yt2 then clipped direct to internal wall, above suspended ceiling in free air, total run about 9m. As above I'll test the drivers and walk away, my job is done, it is now down to the display guys.

If it gets a bit heated on Monday I'll get uncle Glenn to sort him out :rofl:

It might not be cheap drivers but the wrong ones. One thing to look out for is that drivers should not be more than 80% loaded. For example, what is the point of a 100W driver which can consistently only be loaded at no more than 80W.
Personally I think this is a stupid system, but just another spanner in the works. And do as Archy says, if it’s not your fault, charge them for wasting your time.:angel_smile:
 
Ended up getting a call and going back around late this morning! They dont like the digital timers and the lights dont work. Timers taken out and cables Wago-d (new word lol) up. Tested the circuit to make sure, told customer/s that the sockets are fine so call your window display chap. Bill going in tomorrow with extra on it for today.
 
I think I'd put a logging multimeter on the supply for 24 hours just to make sure nothing is affecting the supply had a similar type of problem some time ago and found there was a supply problem the local DNO had a failing joint at the end of the street and the voltage was dropping by 40 - 50v at times for anything from a few seconds to 10 - 15 minutes
 
UNG top recommendation Sir, I did think of the supply for a minuet until I looked down the street with 4 other shops with the same window display system. Theirs are fine, process of elimination = Not the supply. Besides a new data hub just installed and has not gone down yet (data logged for down time by the provider. Nice bloke, good to work with).

Strange how the window display chap has not called me today?

My problem is now sorted so it's up to him.
 
UNG top recommendation Sir, I did think of the supply for a minuet until I looked down the street with 4 other shops with the same window display system. Theirs are fine, process of elimination = Not the supply. Besides a new data hub just installed and has not gone down yet (data logged for down time by the provider. Nice bloke, good to work with).

Strange how the window display chap has not called me today?

My problem is now sorted so it's up to him.

I'm not talking of a complete loss of power but a voltage drop circa 40 - 60v seen it happen quite a few times, thinking back a mate of mine who works on EPOS systems had a problem at home with electrical equipment dying for no apparent reason so he borrowed a mains analyser from work and found he was getting voltage spikes of 1100v for less than one AC cycle the DNO eventually traced the problem to a local substation

Are the 4 other shops window display systems on the same phase as yours though. With the data hub they tend to have power supplies that will work with a wide range of supply voltages so may not necessarily be affected by a voltage drop
 
...and anyway,if it's an estate agent,tell them it is not a "power failure",it's a "current limiting economy feature"....very sought after,these...:stooge_curly:
 

Reply to LED Window Display Problem? in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top