How many spurs can you get off one socket on a ring????? | on ElectriciansForums

Discuss How many spurs can you get off one socket on a ring????? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,278
Reaction score
6,522
Location
Gloucestershire
A friend asked me to have a quick look at the electrics as she wasn't sure if the plasterer was doing it quite right!

On investigation I found the socket (on a ring) was already supplying one spur which fed 2 sockets (JB underfloorboards). The plasterer had already added another spur and then another spur off that spur, and he had another cable in the initial socket ready to feed another spur.

[ElectriciansForums.net] How many spurs can you get off one socket on a ring?????

So altogether the socket was to have 3 seperate spurs taken from it, feeding 5 extra sockets.

Tried to explain it to the plasterer, but he said he'd rang his electrician mate and they had said it was ok. Nice chap though and was quite happy to let me take over. :smile5:
 
A friend asked me to have a quick look at the electrics as she wasn't sure if the plasterer was doing it quite right
WT absolute holy F is going on? What kind of idiot do you have to be to get a plasterer to carry out electrical work.
Tell him from me that both him and his "electrician" mate are complete and utter bloody fools. If they have a problem with that they can come and see me.
 
WT absolute holy F is going on? What kind of idiot do you have to be to get a plasterer to carry out electrical work.
Tell him from me that both him and his "electrician" mate are complete and utter bloody fools. If they have a problem with that they can come and see me.

Subtle, luv it!:beatnik2:
 
WT absolute holy F is going on? What kind of idiot do you have to be to get a plasterer to carry out electrical work.
Tell him from me that both him and his "electrician" mate are complete and utter bloody fools. If they have a problem with that they can come and see me.

I doubt I'll see him again Trev, although he's hard to miss... six foot seven and built like a tank. I still told him he was wrong!! Said it nicely though..

your friend should of just got you to do it in the 1st place

I think you're probably right there.
 
A friend asked me to have a quick look at the electrics as she wasn't sure if the plasterer was doing it quite right!

On investigation I found the socket (on a ring) was already supplying one spur which fed 2 sockets (JB underfloorboards). The plasterer had already added another spur and then another spur off that spur, and he had another cable in the initial socket ready to feed another spur.

View attachment 27480

So altogether the socket was to have 3 seperate spurs taken from it, feeding 5 extra sockets.

Tried to explain it to the plasterer, but he said he'd rang his electrician mate and they had said it was ok. Nice chap though and was quite happy to let me take over. :smile5:

Was there some 'testing' going on here? Wago shorting line and neutral?
 
They do it.
The whole set up see's loadings nothing more than 10 amps for years.
And despite your best efforts, years later,
They can't see what the problem is and simply say
"Its been like it for years, never had a problem" !!!
Give us strength lads, give us strength.
 
Was there some 'testing' going on here? Wago shorting line and neutral?

Yep! Quite a bit!

Has anyone ever actually seen 5 conductors in one terminal in a socket? I've just had a quick look on the forum and I cant see that it is mentioned.. To not have been discussed on this forum which looks into every nook and cranny it must be beyond the realms of even the worst practise!!
 
Yes but they were wired in 1.5 t&e.
Also figure of eight ring mains lovely job, lack of grommets just like yours.
Customer wanted my advise as had reservations about the sparks being used.
Advice !!
Kick him out
Rip it out
Start again.
 
They do it.
The whole set up see's loadings nothing more than 10 amps for years.
And despite your best efforts, years later,
They can't see what the problem is and simply say
"Its been like it for years, never had a problem" !!
!
Give us strength lads, give us strength.

this is normally the quote from the customer when you mention about having to install bonding as well. lol
 
At least the knock out box is a nice deep one. So reduce the OPD to 20A and you will find the plasterer was right all along!! Pah, you lot know nowt!! Seriously though it is pretty bloody silly all in all. I would insist on either damaging walls or lifting floors to get that sorted out. Even if you could squeeze 5x2.5 in a terminal I would not do it.
 

Reply to How many spurs can you get off one socket on a ring????? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top