O

Octopus

Pretty much as the title says - lots of us have opinions but seeing as BEAMA seem to have ruled out plastic CU's lets have a poll - so please add your vote:
 
Have looked at your link and what they say is set to provide even more confusion.
If you look further in the thread you will see references to plenty of ABS boards complying with 61349-3.
But that's only half the story for AMD 3.
They should also be constructed of non combustible material.
So the board manufacturers need to step up to the mark and not simply state the BSEN number.
If they intend for ABS to be a compliant material they need to state constructed from non combustible ABS to BSEN 61349-3.
And that's something they simply are not doing !!

Have to say reading it it's very misleading, and I am sure we will see more of that.
They do cover themselves on page 25 of that document IP2X metal enclosures complying with non combustible materials written in red, have a look.

Link refferred to in post 136 by jay spark
 
Last edited by a moderator:
Have looked at your link and what they say is set to provide even more confusion.
If you look further in the thread you will see references to plenty of ABS boards complying with 61349-3.
But that's only half the story for AMD 3.
They should also be constructed of non combustible material.
So the board manufacturers need to step up to the mark and not simply state the BSEN number.
If they intend for ABS to be a compliant material they need to state constructed from non combustible ABS to BSEN 61349-3.
And that's something they simply are not doing !!

Have to say reading it it's very misleading, and I am sure we will see more of that.
They do cover themselves on page 25 of that document IP2X metal enclosures complying with non combustible materials written in red, have a look.

Link refferred to in post 136 by jay spark


Confusing is what the BS7671 is all about.lol That's why in "non statutory"!lol they can't enforce something that we as electricians argue and debate about constantly.lol But I know what you mean!

The reason they won't say owt is because of all the dollar they are going to make from selling their metal CU's that have been sat in their warehouse, gathering dust.lol If they told us their plastic CU's meet the requirements of AMD 3, then we wouldn't be having these threads.lol


Jay
 
I have read as much on this subject as I can.
And have come to a simple conclusion.
Unless the manufacturers and the IET get together and tell us that they have produced an ABS consumer unit that is classified as non combustible, with the appropriate BSEN number, and making it FULLY COMPLIANT with AMD 3
Then we are going to be left with our heads on the chopping block if we attempt to interpret any other material, other than ferrous steel as non combustible when referring to domestic CUs.
Its very wrong that we are being left with this total mess up.
Its even worse that the powers to be aren't addressing the CAUSE of these fires, or how they compare to other city's around the UK.
Or that the quality of the internal components aren't being improved upon.
But then its like a manufacturer not to admit to faulty materials, and poor connection points, for fear of recompense.
Or scheme providers not admitting to fast track courses that put inexperienced people out there, to fit boards all over peoples homes.
And giving them there trusted logo's with there blessing.
Or what kind of back lash this is going to produce when dealing with existing ABS consumer units.
There are going to be a lot of questions being asked and definitive answers required before any of us go over the trenches into a volley of bullets.
So its keep your heads down.
And lets just see how there going to worm, and explain, there way out of this one.

And as a footnote this surely can leave no doubt, that there IS doubt.

There is no published definition for the term ‘non combustible’ that aligns with the intent of Regulation 421.1.201. However, as stated in Note 1 to the regulation, ferrous metal, such as steel, is deemed to be an example of a non-combustible material.
Steel will no doubt be the material usually employed in the manufacture of the enclosure or cabinet. Nevertheless, it will be open to manufacturers to offer enclosures or cabinets made from other types of material that they claim to be non combustible within the intent of Regulation 421.1.201. In this case, however, the manufacturer would have to provide suitable evidence to support the claim of non combustibility, and it is not presently clear what criteria would be used to judge the non combustibility of a material other than non-ferrous metal.

So there it is.
Unless the manufacturer specifically states the material has been deemed non combustible, it's not.
And more to the point, to date, there not even clear on what criteria they should adopt for anything other than ferrous metal !!
 
Last edited by a moderator:
I have read as much on this subject as I can.
And have come to a simple conclusion.
Unless the manufacturers and the IET get together and tell us that they have produced an ABS consumer unit that is classified as non combustible, with the appropriate BSEN number, and making it FULLY COMPLIANT with AMD 3
Then we are going to be left with our heads on the chopping block if we attempt to interpret any other material, other than ferrous steel as non combustible when referring to domestic CUs.
Its very wrong that we are being left with this total mess up.
Its even worse that the powers to be aren't addressing the CAUSE of these fires, or how they compare to other city's around the UK.
Or that the quality of the internal components aren't being improved upon.
But then its like a manufacturer not to admit to faulty materials, and poor connection points, for fear of recompense.
Or scheme providers not admitting to fast track courses that put inexperienced people out there, to fit boards all over peoples homes.
And giving them there trusted logo's with there blessing.
Or what kind of back lash this is going to produce when dealing with existing ABS consumer units.
There are going to be a lot of questions being asked and definitive answers required before any of us go over the trenches into a volley of bullets.
So its keep your heads down.
And lets just see how there going to worm, and explain, there way out of this one.

And as a footnote this surely can leave no doubt, that there IS doubt.

There is no published definition for the term ‘non combustible’ that aligns with the intent of Regulation 421.1.201. However, as stated in Note 1 to the regulation, ferrous metal, such as steel, is deemed to be an example of a non-combustible material.
Steel will no doubt be the material usually employed in the manufacture of the enclosure or cabinet. Nevertheless, it will be open to manufacturers to offer enclosures or cabinets made from other types of material that they claim to be non combustible within the intent of Regulation 421.1.201. In this case, however, the manufacturer would have to provide suitable evidence to support the claim of non combustibility, and it is not presently clear what criteria would be used to judge the non combustibility of a material other than non-ferrous metal.


And why why do they need to state 'Ferrous' why not non ferrous?
Does this now mean that we are not to use any sort of aluminium enclosure to house MCBs, etc?
 
yes we should start fitting mantel units again haha

joking before any 1 starts
 

Attachments

  • [ElectriciansForums.net] Plastic versas Metal CU's - your chance to vote
    image.jpg
    42 KB · Views: 60
Last edited by a moderator:
All manufacturers' CUs meet this BS. However, Amd 3 calls for all CUs installed in domestic premises to meet BS61349-3 AND be made of non-combustible material.

Thanks ... correct, but you missed the important corollary ... I strongly suspect that the vast majority of CUs, if not all, achieve compliance with BS61349-3 by being self-extinguishing within 30 secs of removal of the 960 deg C glow wire. They cannot therefore claim to be incombustible!
 
Thanks ... correct, but you missed the important corollary ... I strongly suspect that the vast majority of CUs, if not all, achieve compliance with BS61349-3 by being self-extinguishing within 30 secs of removal of the 960 deg C glow wire. They cannot therefore claim to be incombustible!

Whilst I totally understand this point, self-extinguishing and non-combustible have subtly different meanings. More pertinently, this is all semantics. In real terms the only option we have at the moment is a metal CU, or a metal/masonry enclosure around said CU.

The terms used and the way this has been done is wrong, I know - in fact, we all know. However, realistically the intention of this reg has been clear from day one, and I think it's about time we just accepted that it's happening and make the best of it.
 
It was mentioned to me that the next version of the Regs will give guidance on where these non combustible super metal boards should be stuck in a house. It was said that they will have to be sited by exit doors so homeowners can watch them smoldering and catching fire.

I do do wonder sometimes if these electrical organisations deliberately suggest a woolly and vague Reg amendment so it can then be thrashed out on various forums and then they can then make future Reg changes.


As 'official' comment has been made about connections not being tightened and thus the cause of these CU fires it would be nuts if the industry doesn't go back to twin screw terminals.
 
This 2 screw terminal business....agree. Problems occurred because of change over to mcb's, which only have the one terminal screw, a different type altogether.

'Oh, well we might as well make N and E a row of single screw terms on a sliver of brass ' save a chunk on production cost.....and who even mentioned it at the time?
 

Reply to Plastic versas Metal CU's - your chance to vote in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Poll
Happy belated........young pup:cool: First voted in a general election the year after you came along, 50 back.
    • Funny
    • Winner
    • Like
2 3
Replies
39
Views
2K
G
  • Article
Best Tile Adhesive for Walls and Floors? Voting is now CLOSED - Results are in!! Well done MAPEI! Which Tile Adhesive Did You Use Most During...
Replies
0
Views
46
Gazzer
G

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top