just a quick one doing some rcd tests today, and at x1 value the tripping time was 46mseconds and at x5 29mseconds now i no that as long as at x5 value is under 40mseconds all is ok just thought the x1 value was a bit high so my question is there a max value for times 1 as i must admit not had x1 values that high before your thoughts please
 
There all the same those switchy things than the wires go in. I only use the ones with 40 on them cause its my favourite number.
 
but if the wirral was in wales, would there be enough sheep to go round?

would the sheep need the wellies to cross the dee estuary?
 
just a quick one doing some rcd tests today, and at x1 value the tripping time was 46mseconds and at x5 29mseconds now i no that as long as at x5 value is under 40mseconds all is ok just thought the x1 value was a bit high so my question is there a max value for times 1 as i must admit not had x1 values that high before your thoughts please

What is the point of conducting tests if you do not know what constitutes a good or bad result?
 
but if the wirral was in wales, would there be enough sheep to go round?

would the sheep need the wellies to cross the dee estuary?

I had my way the would be razor wire across the border and any bugger trying to get across it into England would be shot.

There again I could take solence in the fact I catch a Welshman inside Chester city walls after 6 at night I can legally kill him as long it is with a bow and arrow.
 
I'm big enough to admit my mistake just for the record they are bs 61009

Then they are not BS. It is BSEN 61009 300ms max 1x and 40ms max 5x. A BS type (4293) would be 200ms max 1x and 40ms max 5x. Wait until you test an MEM 30ma RCD, for whatever reason they are often 100+ms on 1x and only just scrape in under 40ms on 5x.
 
I had my way the would be razor wire across the border and any bugger trying to get across it into England would be shot.

There again I could take solence in the fact I catch a Welshman inside Chester city walls after 6 at night I can legally kill him as long it is with a bow and arrow.

Wow that was intense

Its probably best now to have the cheques sent by post
 
I always found that hager boards that are around 10 - 15 years old, the 1x usually comes out at around 135ms, only ever seen it on these boards, and interestingly my hager board of the same era (2000) does exactly that, but the newer ones are 30 - 40ms.

I have to say I always make a note on the cert, although its perfectly acceptable and within, make a note that it's on the higher end of what I would like to see, but nothing needs to be done. I guess I just make a note on an observational level in case the next person questions it and has my paperwork to hand.
 
The dimmers I install used to have hager RCDs in them and they were always in the late hundreds for x1 trip times.

They use Eaton parts now since Eaton bought the company (cooper controls) that own the company (zero88) that manufacture them. Funnily enough zero88 are welsh! (As far as I know they still are)
 

Reply to rcd tripping times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
My MFT auto mode will do the 5*In anyway so easier to just keep resetting until test is done... As an aside, I have seen different trip times...
Replies
12
Views
2K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
636
  • Question
I've never come across this fault, but a faulty breaker seems most likely to me
Replies
2
Views
1K
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K
  • Question
As you said in #9 get an electrician involved. The information you are giving is not clear as you do not understand what is being asked which...
Replies
10
Views
984

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks