Hi,

ok ok so I tested this old 3036 board a week ago ready to change today, all ok, nothing bad.

went today to change the board, changed it all etc, had to extend two legs, but other than that, nice job.

i go to switch it on prior to testing like you do, and one of the RCDs won't hold.

bugger, what have I done? Scratching head...

tested IR and its 0.02 between neutral and earth, so I think maybe I missed something previously, I quickly removed a few faceplates as there were only 6 sockets on that ring as it happend, nothing obvious.

anyway, so I think I'll try continuity between Earth and neutral at one we of the ring and got 0.61 and did it the other end and it was 0.02, so I think, that's a bit sodding close to the board, what could it be?

so I start t remove that circuit from the board thinking maybe of done something strange with a joint where I'd extended the leg... Nothing.

so I stand back and think what the heck is it, then I think hang on those shelves weren't there before.... Three large oak shelves, in the return on the wall directly sbove the fuse box....

i thought, I wonder... So got the meter out and touched it on a screw head on the bottom shelf and would you sodding believe it I had continuity!!!

anyway, so I removed the screw and it resolved my problem...

Customer later returns home, says everything ok? I said yes, it is now...

i said they are nice shelves, did you fit them? No we had someone do it for us.... I said tell them they drilled through a cable.

thete were probably 8 cables going straight up the wall where he had drilled 3 holes so not sure how he managed to miss the others, luck I say!

anyway...
 
Seriously, if you change a DB or CU I don't see how testing before the replacement means it's unnecessary again after the work is complete. I'd say this is bad practice and borderline dangerous and unnecessarily reckless, it's certainly not the kinda thing I'd leave unchallenged on a forum with a heavy trainee contingent and I'd suggest even if the UK regs don't specifically require it you should always spend the extra 2 or 3 minutes and test before making live.
 
Seriously, if you change a DB or CU I don't see how testing before the replacement means it's unnecessary again after the work is complete. I'd say this is bad practice and borderline dangerous and unnecessarily reckless, it's certainly not the kinda thing I'd leave unchallenged on a forum with a heavy trainee contingent and I'd suggest even if the UK regs don't specifically require it you should always spend the extra 2 or 3 minutes and test before making live.


At no point did I say I didn't test it afterwards. I tested before hand, changed it, energised it, he led everything worked, then continued with the testing.

So just to make it clear, I do test all my work thanks.
 

Come on, you're an experienced member who knows what this place is like and you stated that you changed a CU because it was a crap 3036 board which was hanging off the wall. Did you seriously expect not to get stick?

If you had changed the board 'after discussing the merits of adding RCD protection as part of the larger job of extensive alterations to the installation' then there would likely be no reaction at all.
 
Come on, you're an experienced member who knows what this place is like and you stated that you changed a CU because it was a crap 3036 board which was hanging off the wall. Did you seriously expect not to get stick?

If you had changed the board 'after discussing the merits of adding RCD protection as part of the larger job of extensive alterations to the installation' then there would likely be no reaction at all.

accepted, i suspect everyone has there way of doing things and things they perhaps shouldn't share due to getting stick. I have said the cable is being replaced.

ill keep quiet now.
 
it's OK. UK. you're amomg friends here:
.
.
.
.
.
,
,
,

.
.
.


[ElectriciansForums.net] Neutral Earth Fault
 
but did he IR test the rigging? it might be shorted to the mast.

That I don't know,
but does the mast have an RA of less than 200 ohms ? ;)

Poor old UK is walking the plank, E54 with the sword behind him, and Tony with the cosh lol :)

H69 strapped to the front as a figure head lol, on the good ship Electrical forum lol :)
 
....I'm going to give UKsparks a break...i love an under-dog...

His honest enough post has got scent in the hyeenas nostrils...yep,we all know,or should,the correct sequence of events,and whilst these may not have been adhered to,there are lots of other rules,in instances such as this,such as not being legally able to prevent the home-owner saying "i want it on" or "I'm turning it on..."

The comment regarding trainees viewing such details is fair,although their instruction should not leave no place,for a bit of "real-world" input,and being capable of judging the rights and wrongs of said details.

The man who never made a mistake,never made anything :icon12:
 
....I'm going to give UKsparks a break...i love an under-dog...

His honest enough post has got scent in the hyeenas nostrils...yep,we all know,or should,the correct sequence of events,and whilst these may not have been adhered to,there are lots of other rules,in instances such as this,such as not being legally able to prevent the home-owner saying "i want it on" or "I'm turning it on..."

The comment regarding trainees viewing such details is fair,although their instruction should not leave no place,for a bit of "real-world" input,and being capable of judging the rights and wrongs of said details.

The man who never made a mistake,never made anything :icon12:

There is when a certificate is too be issued and signed by myself.
 
The Main issue for me is that dead tests should have been carried out before energising the board forget the customer wanted is house back on, That's tough he is not the professional. The 2nd issue and probably more serious is that the damaged cable as been left damaged and even worse as been left energised.
 
I'm not knocking you, but this fault should have showed up when you did the dead tests before energising the installation.

I know, I know its my fault, I do usually fully dead test at the point of changing the board, I guess with this, I had dead tested the week before which is why I jumped a step to just check everything was working as expected, and was then going to dead test.

I hold my hands up to this.
 
I know, I know its my fault, I do usually fully dead test at the point of changing the board, I guess with this, I had dead tested the week before which is why I jumped a step to just check everything was working as expected, and was then going to dead test.

I hold my hands up to this.
Every day's a learning day. Just learn from it and move on.
 

Reply to Neutral Earth Fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
359
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
823
  • Question
Must be thousands of installs like this. No wonder so many company’s jumped on the solar bandwagon and just threw them in. I’ll get mine changed...
    • Like
Replies
23
Views
4K
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
359
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks