OK guys, need some advice/opinions please.
Just been out to have a quick look at a fairly big 5 bed house that is being converted into a 6 bed multi let near a hospital.
The landlord is having a combi fitted, but wants to put 4 electric showers in. 1 in the bathroom and 3 en-suites.
Looks like there is one ring for the house (up & down) one for the kitchen and ground floor extension, 2 lighting circuits and cooker circuit.
Main fuse appears to be 100a. It was a very quick whistle stop visit.
When I do the max demand calcs, I can't get anywhere near 100a, even using 0.4 of every circuit other than the highest, and that's without any additional circuits that he may want installing.
I suggested having at least 1 shower off the combi but he seems very reluctant to do it.
In the real world, would this be in your opinion, too great a load for a 100a fuse?
Just wondering what your thoughts were?
Thanks guys n gals
 
Depending on what type of landlord he may be...it's either 3ph...or six laminated posters,giving the time slots that showering is permitted...:icon12:
 
A 6 bed multi let, i bet that's gonna be fun each time the electric bill drops through the letter box!!

They should fit these pound coin meters to each room haha
 

Attachments

  • [ElectriciansForums.net] 100a supply advice???
    image.jpg
    124.1 KB · Views: 210
OK guys, need some advice/opinions please.
Just been out to have a quick look at a fairly big 5 bed house that is being converted into a 6 bed multi let near a hospital.
The landlord is having a combi fitted, but wants to put 4 electric showers in. 1 in the bathroom and 3 en-suites.
Looks like there is one ring for the house (up & down) one for the kitchen and ground floor extension, 2 lighting circuits and cooker circuit.
Main fuse appears to be 100a. It was a very quick whistle stop visit.
When I do the max demand calcs, I can't get anywhere near 100a, even using 0.4 of every circuit other than the highest, and that's without any additional circuits that he may want installing.
I suggested having at least 1 shower off the combi but he seems very reluctant to do it.
In the real world, would this be in your opinion, too great a load for a 100a fuse?
Just wondering what your thoughts were?
Thanks guys n gals

My thoughts???

The man is clearly a fool.

WHY would anyone choose an electric shower - of any size - over a decent pressure balanced or (better) thermostatic shower running off a combi??
 
Hi guys,
thanks for the replies,
just a little update,
I told him I was only prepared to install 2 showers max, which he accepted, and has subsequently decided to install a much larger boiler and have ALL mixers, which solves the shower problem entirely.
Regarding the metering question, the gas & electric is included in the rent, and yes, there is a fire alarm system being installed, as is emergency lighting.
Thanks everybody who took the time to reply.
Until next time :)
 
If it is a separate CU per property, cost up how much it would cost to have a MID certified meter feeding each property, and explain to the landlord the extra cost of meters now compared to later.
 
If it is a separate CU per property, cost up how much it would cost to have a MID certified meter feeding each property, and explain to the landlord the extra cost of meters now compared to later.
Re MId metering....i know nothing about them. I did ask in here last week, but without much success. Any pointers where to find info out about them. Are they becoming law in certain situations?
 
Re MId metering....i know nothing about them. I did ask in here last week, but without much success. Any pointers where to find info out about them. Are they becoming law in certain situations?

Any meter used for the billing of electricity must be MID Approved under Annexe MI-003. Existing OFGEM meters are still legal and can be installed until October 2016, after which date every meter used for billing must be MID approved.
The Measuring Instruments Directive (MID) was introduced by the European Commission in 2004 to promote the free trade of measuring instruments throughout Europe and provide common rules for their use. The European Directive 2004/22/EC, MID came fully into force on 30th October 2006.


Here you go mate.
 

Reply to 100a supply advice??? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
271
tommyh311
T
T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
208
Tommyh311
T

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top