Hi,

I changed a CU this morning, old 3036 for split board.

I had tested it prior, IR etc, few Zs readings and the like, continuity of rings etc, nothing abnormal, even checked for borrowed neutral on light circuit which there was.

Anyway, changed it this morning, put lights on one rcd and the sockets on another.

Tested everything, R1+R2, IR etc on all circuits and other tests, all absolutely fine, tested every point on each circuit, all readings all ok.

Turn it on after completing all tests...

Everything seems ok, thats good then, walk round the house, switch lights on upstairs so see if they all work as expected, yep, all fine, all fine downstairs, but when it comes to the hall light (not stair light) i turn it on and it trips both RCD's? hmm thats odd. Take the bulb out and its fine.

So i put my meter on it on line neutral and earth, 230 L-N, 230 L-E, 0 N-E, ok so I would imagine the bulb would work.., put it in switch it on again and it trips both.

Anyway, I narrowed it down, it appears there is a link between the socket circuit and that light fitting.

That light fitting is definately on the light circuit.

I even then tested N-E from the socket circuit, so see if theres any reading (dead) at the light, nothing, I tried all combinations, I get zero voltage at the light fitting when the light is off and also when the light MCB is off.

So somewhere, and for some reason that particular light is connected, but cannot seem to do any tests that suggest it is.

Unless I have missed the obvious.

Anyway, so resolve it until monday, I just moved the lights over to the same RCD as the sockets, then on monday will look at it as have got to pull the floor up to add more sockets in anyway.

I was happy to a degree that it was safe to leave for the weekend as I could not get however much I tied any voltage on that light fitting when the lights were off at the CU.

The point to this I guess is, if I had put them both on the same RCD to start with which I may have done, it was just chance I didn't, then I would never have found this problem.

Any thoughts? I can only see that it is connected on the neutral, but can't understand why as when you disconnect the socket circuit at the board, the light still works fine...

Bit of a weird one, I have not had this happen before.
 
Not that old chestnut again, that cable got fixed, see photo below, was very minimal damage to be honest, but still repaired it.

[ElectriciansForums.net] Link between one light fitting and socket circuit?[ElectriciansForums.net] Link between one light fitting and socket circuit?[ElectriciansForums.net] Link between one light fitting and socket circuit?
 
It's just a matter of doing all your tests now UK, interesting though. Look forward to the update :smile5:

The thing with this is that I nor anyone else would have picked this fault up unless they had the light switch on with a bulb in that lamp holder and did an IR between the sockets snd lights. There's a limit as to how much you can test and that is one that I didn't do.

i won't bite at this but as I couldn't seem to get a voltage reading at the light however much I tried with the light circuit off, I'm not bothered about leaving it until next week. It's been like it probably since the house was built in the 80's anyway.

I was 20 miles from home, and had no means to rip floor boards up, nor was I in the mood to be doing that, especially as its all laminate anyway.
 
Not that old chestnut again, that cable got fixed, see photo below, was very minimal damage to be honest, but still repaired it.

Yes, that old chestnut again because you left a job in a dangerous state rather than fix it.

There’s an echo follows you around, it’s faulty/dangerous, I’ll do it next week.
 
Yes, that old chestnut again because you left a job in a dangerous state rather than fix it.

There’s an echo follows you around, it’s faulty/dangerous, I’ll do it next week.

And you fix everything thete and then do you? the installation is no worse than when I found it, if anything it's safer, I'm not entering into am argument about this.
 
And you fix everything thete and then do you? the installation is no worse than when I found it, if anything it's safer, I'm not entering into am argument about this.

Generally speaking I will fix, or at least diagnose and temporarily fix faults there and then. What I definately don't do is go telling the whole world about any little bodge I may have to do on the spur of the moment. Sometimes I phone my mentor who taught me the trade for a bit of advice or a second opinion.
 
The thing with this is that I nor anyone else would have picked this fault up unless they had the light switch on with a bulb in that lamp holder and did an IR between the sockets snd lights. There's a limit as to how much you can test and that is one that I didn't do.

i won't bite at this but as I couldn't seem to get a voltage reading at the light however much I tried with the light circuit off, I'm not bothered about leaving it until next week. It's been like it probably since the house was built in the 80's anyway.

I was 20 miles from home, and had no means to rip floor boards up, nor was I in the mood to be doing that, especially as its all laminate anyway.

I agree it is something that I would not have found with any standard testing, it would have showed up pretty quick though once the new cu was fitted as I fit SPSN RCBOs for all circuits as standard.

You shouldn't be ripping floorboards up whatever mood you are in! A tradesman should be carefully lifting them so as to cause the minimum possible damage. Ripping people's houses apart is what demolition contractors and plumbers do.
 
I accept that, but it's not being left, it's going to be fixed.

you keep your bodged or temp knock ups etc to you and your friends down the pub and I'll continue to post the odd thing on here, I knew I'd get stick for bringing it up.
 
I agree it is something that I would not have found with any standard testing, it would have showed up pretty quick though once the new cu was fitted as I fit SPSN RCBOs for all circuits as standard.

You shouldn't be ripping floorboards up whatever mood you are in! A tradesman should be carefully lifting them so as to cause the minimum possible damage. Ripping people's houses apart is what demolition contractors and plumbers do.

I hsve to say this has caught me out as didn't pick it up, and it's only by chance it's to come to light as they were on different sides of the board but could very easily have been on the same side then I would never have known.

Ive got three more boards lined up for this month so will look a bit deeper at the pre testing to try to eliminate anything like this again.

as forge comment about ripping the floor up, it was just an expression.
 
You'll not catch something like this on pre-change testing. Not unless you are going to spend more time devising bizarre tests than actually doing the job. You just have to suck it up sometimes and hope you've allowed enough contingency in your price. If not then you just have to accept that some jobs go wrong and make a loss, shyte happens sometimes and you just have to accept it.
 

Reply to Link between one light fitting and socket circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Or just save all the agro and get a proper sparks round for 45 minutes to test the supply cable and re-fit the socket 'properly'
2
Replies
19
Views
2K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
577

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top