J

Jake1579

Im on an electrical installation course in college and currently on a 3 month trial as an apprentice so thats why im asking zs testing from what i understand in college they teach it you as zs=ze + r1/r2 which i understand but when i go and actually look at zs test myself say on youtube they talk about like for example a ligthing circuit to test it at the switch line and the earth on the celing rose or light switch depending if its awkward to get to but they say test at the last lighting point so my questions are
1. why do you need to test at the last point?
2. does this test take in to account the ze and r1/2?
 
Because it can be safer, but it seems we're going around in circles now.

Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...
 
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...

Depends on the circumstances.
 
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...
Who said anything about Ze? Why would you not be able to take a live Ze reading? And how else would you take it?
 
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry.

There IS something very wrong with the industry unfortunately.

What if you were using metallic containment as the CPC?

Measure is the only solution.

Why arse around calculating when you can directly test/measure the Zs at any given point on the circuit, and get an accurate value into the bargain!!!

Because it can take hours to get ISO locks taken off and reinstated.

And you can get accurate results with a brew in your hand rather then an MFT.
 
There IS something very wrong with the industry unfortunately. Agreed!!



Measure is the only solution. Are you having a laugh or what??

Because it can take hours to get ISO locks taken off and reinstated. So how are you going to take dead test values to calculate??

And you can get accurate results with a brew in your hand rather than an MFT.

I'll guarantee that any calculated value you come up with, will not be the same as the live measured value!!
And coupled to this new convoluted Zs measurement, where it seems you need to know the bloody voltage, even less likely... lol!!
 
Why is calculating Zs theoretical? You have measured the Ze and R1 R2 using a calibrated meter.

Just do the maths.





(Tin hat on) I know I'm in the minority here....

Because the maths takes no account of parallel paths and does not give the true reading.

Are all parallel paths permanent?
depends, an install we did had that much steel bolted together and that many swa cables that the results were way better than they should have been, because of the design of the building most steel work was directly connected without bonding cables
 
Surprised no one has mentioned the inaccuracy of 'no trip' ZS tests yet. I seldom get a measured value lower than a calculated when on 'no trip'.

A valid point that i didn't consider, as we initially temporarily install spare double pole, TP+N breakers/ isolators, only installing the RCD units at time of testing the RCD's. So i'd say 95 % of all our circuits Zs testing is carried out at full current...
 
Surprised no one has mentioned the inaccuracy of 'no trip' ZS tests yet. I seldom get a measured value lower than a calculated when on 'no trip'.

Surprised that no one has mention that you can get your Ze "by enquiry" then test for Voltage, dead test R1+R2.

If the Ze = 0.17
R1+R2 = 0.54
V = 237

Only two tests needed lol

Zs = 0.17 + 0.54 = 0.71
PFC = 237 / 0.17 = 1.39kA

All the maths are thrown out of the window soon as you get the MFT out. The test results will never match the maths in the real world and should only be used as a calculated/estimate of results before testing to compare against.

With the things we have these days like socket adapters and Lightmates, no reason not to safely carry out tests.
 
Cant really explain it any better or clearer than this.

Firstly my apologies for interrupting a thread. I'm an avid reader of forums but not well versed with any etiquette .
I have particularly sought to seek your advice as I deeply respect your knowledge and understanding of the 2394/5 examinations.
I am undertaking the 2394 written exam in a few weeks and have been just finalising my revision notes. I have made use of the published Chief Examiners Reports which do tend to point out the basic errors students make.
However one note from a report (Aug 2014) is confusing me, and I would be grateful for your thoughts.
To quote from the report :-
"Candidates were asked to explain the expected pattern of test results when carrying out an earth fault loop impedance measurement at each socket-outlet on the ring circuit. Many candidates incorrectly believed that the results would be the same at each socket-outlet. "
Please correct me if wrong but I have been taught that a correctly installed ring circuit will have substantially the same (R1 + R2) value at each socket outlet (within 0.05ohms). The only exception would be where the ring contains a spur , the (R1 +R2) being marginally higher at this point , proportional to the extra cable length.
I have also been taught that the following calculation is used to calculate Zs , Zs = Ze + (R1 + R2). I'm fully aware of ambient temperature and conductor operating temperature considerations for verification but lets keep it simple for now. Ze is a constant, as mentioned (R1 + R2) should be substantially the same for each outlet so my question is why would it not be conceivable to expect substantially the same Zs values ?
Again my apologies for interrupting this thread, I would be really grateful for thoughts .
 
Firstly my apologies for interrupting a thread. I'm an avid reader of forums but not well versed with any etiquette .
I have particularly sought to seek your advice as I deeply respect your knowledge and understanding of the 2394/5 examinations.
I am undertaking the 2394 written exam in a few weeks and have been just finalising my revision notes. I have made use of the published Chief Examiners Reports which do tend to point out the basic errors students make.
However one note from a report (Aug 2014) is confusing me, and I would be grateful for your thoughts.
To quote from the report :-
"Candidates were asked to explain the expected pattern of test results when carrying out an earth fault loop impedance measurement at each socket-outlet on the ring circuit. Many candidates incorrectly believed that the results would be the same at each socket-outlet. "
Please correct me if wrong but I have been taught that a correctly installed ring circuit will have substantially the same (R1 + R2) value at each socket outlet (within 0.05ohms). The only exception would be where the ring contains a spur , the (R1 +R2) being marginally higher at this point , proportional to the extra cable length.
I have also been taught that the following calculation is used to calculate Zs , Zs = Ze + (R1 + R2). I'm fully aware of ambient temperature and conductor operating temperature considerations for verification but lets keep it simple for now. Ze is a constant, as mentioned (R1 + R2) should be substantially the same for each outlet so my question is why would it not be conceivable to expect substantially the same Zs values ?
Again my apologies for interrupting this thread, I would be really grateful for thoughts .
you're slightly confused here. when cross connecting the RFC legs, you should get R1+R2 at each outlet will be the same. your Zs readings are taken with the RFC legs connected into the supply, so will be dependent on the resistances when in this configuration. i.e, highest reading will be at thew mid point.
 
you're slightly confused here. when cross connecting the RFC legs, you should get R1+R2 at each outlet will be the same. your Zs readings are taken with the RFC legs connected into the supply, so will be dependent on the resistances when in this configuration. i.e, highest reading will be at thew mid point.
Now why couldn't I have thought of that much easier explanation instead of drawing this diagram!
[ElectriciansForums.net] zs testing
 
Thank you for your reply, makes perfect sense . I will bring it to the attention of my tutor as ironically the very same question came up in a mock paper we went through before the Easter break . There were differing views as to the answer. Again, many thanks.
 

Reply to zs testing in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top