Hi all

https://www.dropbox.com/sc/vpnieno3z1xuxna/AAA_qOcvnyVCb-ZRiBAtQFb1a
https://www.dropbox.com/sc/naxnji157w6chkt/AAABxHKzpVMWPUElrt-d6fQga

Does this comply with BS7671?
They are posisioned within 700mm of a shower within a wetroom. Within zone 1 - no permanent fixed partition! with no basin!

I note that these are electronic switching with the 230v supply into the rear of the switch!

I note regulation 701.512.3: In Zone 1: only switches of SELV circuits supplied at a nominal voltage not exceeding 12a.c. rms or 30v ripple free d.c. shell be installed, the safety source being outside zones 0, 1, 2
 
Probably not compliant then, though reasonably safe as it would require a concerted effort to spray water on them.
I assume you have taken the distance of the barrier into account as well for the 700mm measurement.
Was it converted to a wet room from a shower?
 
Yes it was a shower room - the distance from the shower screen (movable) is 300mm
Distance from water outlet to screen is 400mm

This work was done by a plumber
He also installed an electric U/F heating Mat - No iso and the below pic - found in the attic
https://www.dropbox.com/sc/m7j7ju3ehy1qmae/AAAxpLXCSSfNRa_J8NU4yyQ7a

also this in a cupboard next to the oven
https://www.dropbox.com/sc/vq3whaup495xwb2/AADWPDnnMp3YZpGswPyrgptUa
He charged £175 to change the oven and this lovely job!
For the bathroom he charged well over £2,000.00
 
Last edited:
The distance could then be compliant as you have to take into account any barriers (assuming they are up to 2.25m)
[ElectriciansForums.net] Does this comply - Zone 1
The rest of the pictures are abysmal, it seems he is short on earth sleeving and junction boxes!!
 
The distance could then be compliant as you have to take into account any barriers (assuming they are up to 2.25m)
View attachment 29027
The rest of the pictures are abysmal, it seems he is short on earth sleeving and junction boxes!!


No the barrier is not upto 2.25m - it is only about 1.8m
Also the bottom of the barrier starts at about 1m off the floor.
This barrier can swing from side to side - I thought this rule only applies to fixed barriers not non-fixed
 
Overall the work is not good quality.
I think the barrier is a fixed permanent partition it cannot be removed and would provide a barrier wherever it was unless it can fold back into the shower cubicle.
However the height means it is not relevant.
Poor work high cost.
 
Sorry to reopen this, need a hand with a quick question I cant answer
Same property - the Electric underfloor heating has only been installed in zone 1 (in the shower area of the wetroom)
Does this comply?

I have checked the regs but cant find anything suggesting either way.


Any help is greatly accepted.

Before anyone asks I dont have any spec on the E-UFH, all I know is the control (seen in post 1) switches 230v A.C. to the mat and has a thermostat buried (in the floor - I can only guess!) The cables are already buried in the wall after a plumber attempted and hashed it up!

This E-UFH is layed upto 2 inches from the drain
 
Last edited:
As far as the actual under floor matt goes, its under the floor therefore I would not class it as in a zone rather in a location containing a bath or shower - however it should be RCD protected and have an earthed grid/sheath.
 

Reply to Does this comply - Zone 1 in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Wales

Thread Information

Title
Does this comply - Zone 1
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top