Hi,

I have a question I would like to put to you to see who does what really.

The majority if not all manufacturers state something about the fan must be fused down to 3A...

Ok, scenario...

You have a bathroom, 6A light circuit, the light can either be switched at pull cord, light switch outside or the light fitting.

The customer says they want an extractor fan with Timer.

Option One
Do you just fit a fan in the ceiling / wall, and connect it off the light circuit straight to it and think nothing of it? This would be a permanent live supply and switched live.

Option Two
Do you fit a fan, and put a 3A fuse on the permanent live only? Leaving the switched live on 6A, also leaving the fan with the possibility of a blown fuse scenario but also having a live supply to it. You also fit a 3 pole fan isolator.

Option Three
Do you fit a fan, and put a 3A fuse on the permanent live supply to the light, then use that for the live for the fan, and the switched side of the light for the switched live etc. You also fit a 3 pole fan isolator.

Just to add to this
On top of these three options, lets say this is downstairs, no loft space etc, brick walls. You need to put a 3 pole isolator somewhere, where do you put it? Do you surface mount it in a box? Do you use a 3 pole pull switch on the ceiling? But hang on, where do you then put the 3A fuse? Do you not bother? Do you put in on the surface or ceiling?

Just wondering what others do as have been having this conversation with a couple of people. I also rang Manrose about this about putting a 3A fuse across the switched live too, they said, although preferable, it only really needs it on the permanent live.
 
option 3 and fit on the surface mounted 2g (2x1g) pattress by the door/ on the outside of the door

or if you want to be overcomplicated don't use the light as a sl because sometime in summer people don't use lights/ need lights, fit a separate pull cord just for the fan so they can switch the fan on separate to the light. (If for use in a shower room)
 
Last edited:
option 3 and fit on the surface mounted 2g (2x1g) pattress by the door/ on the outside of the door
or if you want to be overcomplicated don't use the light as a sl because sometime in summer people don't use lights/ need lights, fit a separate pull cord just for the fan so they can switch the fan on separate to the light. (If for use in a shower room)

Excel 3 Pole Fused Fan Isolator Switch - White | QVS Electrical Wholesalers

Corbs have you seen these? Not as obtrusive as having 2x1gang pattress or a dual pattress.
 

Attachments

  • [ElectriciansForums.net] Fusing down of extractor fans
    image.jpg
    54.4 KB · Views: 368
I don't see much wrong with reliance on the 5/6 amp OCPD. Have never seen a fan go up in flames nor heard of one doing so. One good thing with AMD3 is the slight change regarding how we have to view and take into account MIs.

I stand to be corrected on this. So tin hat at the ready!
 
Agree with someone else's post above - why have the fan coming on with the light at all?? Half the time we have a shower it's still daylight so the lights don't get switched on. We just use the pull cord on the fan. Daz
 
i generally wire fan independent of the light. apart from the advantage in DPG's post, it also means you don't have to have a noisy fan waking everone up at 2 a.m. when you go to recycle your ale intake.
 
i generally wire fan independent of the light. apart from the advantage in DPG's post, it also means you don't have to have a noisy fan waking everone up at 2 a.m. when you go to recycle your ale intake.
But on the other hand it'll drown out the sound of the release of excess gases and remove the stench to boot lol!
 
I don't see much wrong with reliance on the 5/6 amp OCPD. Have never seen a fan go up in flames nor heard of one doing so. One good thing with AMD3 is the slight change regarding how we have to view and take into account MIs.

I stand to be corrected on this. So tin hat at the ready!

Could you expand on that a little GayOwl?

I think you're referring to 134.1.1?

If you are then I can see the difference in the wording of the reg compared to the BGB, however..

"The Installation of electrical equipment shall take account of the manufacturers instructions"

Does that still mean we HAVE to follow MI's as in the previous 134.1.1 or does it mean we can now give it 'consideration', and if we deem the install to meet all other regs and to be safe we do not have to follow MI's?
 
Could you expand on that a little GayOwl?

I think you're referring to 134.1.1?

If you are then I can see the difference in the wording of the reg compared to the BGB, however..

"The Installation of electrical equipment shall take account of the manufacturers instructions"

Does that still mean we HAVE to follow MI's as in the previous 134.1.1 or does it mean we can now give it 'consideration', and if we deem the install to meet all other regs and to be safe we do not have to follow MI's?
The previous regulation stated must be installed in accordance with the manufacturers instructions, however this is patently ridiculous for minor items such as light fittings where the manufacturer does not write comprehensive installation conditions (and often get it wrong), it may be much more sensible for complex items of integrated equipment, however the manufacturer cannot cover all eventualities so some level of autonomy should be given to the installer.
As 510.3 states take account of manufacturers instructions they are simply aligning the two differing regulations so that there is concordance between them.
Taking account of the instructions means that you must make a conscious decision not to follow them for well founded reasons, such as regulatory compliance! But you must know what they are and why you are not following them.

As they say, if all else fails, read the instructions!:smile5:
 

Reply to Fusing down of extractor fans in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Interesting document thanks. But it neglects the half-wave rectification, and also totally neglects the effect of the coil inductance when...
2 3
Replies
31
Views
3K
  • Question
I think you are going to need an electrician because it looks like someone has used the bare earth (has been sleeved black) as a live conductor...
Replies
1
Views
821

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Market Harborough

Thread Information

Title
Fusing down of extractor fans
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
52
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top