Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from first and second rod combined: 6.3 Ohms
[ElectriciansForums.net] Todays Earth Rod Efforts

Reading from all three rods connected together: 3.2 Ohms
[ElectriciansForums.net] Todays Earth Rod Efforts
 
Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
View attachment 29132

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
View attachment 29134

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
View attachment 29133

Reading from first and second rod combined: 6.3 Ohms
View attachment 29135

Reading from all three rods connected together: 3.2 Ohms
View attachment 29131


Good work. Bet you only get down to 1.5 ohms with the next rods driven in mate....sods law I think we call it! You could always put any RFCs on a 20A and tell them they can't use their electric shower and hob!! Tell them disconnection times are very very important!! Look forward to the update mate.

Neil
 
No a load of rubbish, pull them all out and start again!!:mad2::53:

I would say 3.2Ω is a pretty good reading, 71A fault current enough to trip a 10A MCB.
Pretty close to the resistors in parallel results actually which is interesting to know.
Thanks for putting in the effort to give us some feedback.
 
I think I'll put two more locations in and end it there, I bet each will knock an ohm off the figure.

it about killed me off beating them in with a lump hammer!

By the time the group has settled the reading will have got better as its really only the bottom rods that are in are touching the earth as the others are flapping round due to the couplers.
 
The first one was easy, the second was a little touch, but the third rod was the killer, the deeper you go, it just gets sodding hard work.

I need to achieve a higher fault current really as 71A is pants, just looking at the time current tables in the BYB and max zs etc.
 
I applaud your efforts with this one I really do. Looks like you will end up with something close to very good.

I have to say though, driving coupled rods with a lump hammer..... don't you like yourself very much ?
 
I think I'll put two more locations in and end it there, I bet each will knock an ohm off the figure.

it about killed me off beating them in with a lump hammer!....
You must be mad, get an attachment for a jackhammer. Also if you want a better Ra go 1 rod deeper on all your existing locations rather than making new locations.

By the time the group has settled the reading will have got better as its really only the bottom rods that are in are touching the earth as the others are flapping round due to the couplers.[/QUOTE]
 
You must be mad, get an attachment for a jackhammer. Also if you want a better Ra go 1 rod deeper on all your existing locations rather than making new locations.

By the time the group has settled the reading will have got better as its really only the bottom rods that are in are touching the earth as the others are flapping round due to the couplers.
[/QUOTE]

I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.
 
I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.[/QUOTE]

or one of these :D much easier

[video=youtube;vvCZvNj8H30]https://www.youtube.com/watch?v=vvCZvNj8H30[/video]
 
Last edited:

Reply to Todays Earth Rod Efforts in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Sorry for the late response but by the NEC code book requires one ground rod near the panel and another ground rod at least 6 feet or more using #...
Replies
1
Views
871
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
926

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Market Harborough

Thread Information

Title
Todays Earth Rod Efforts
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top