Hi all.

usaul story, first fixed a new build now boarded and skimmed. Customers has now gone to howdens to get the kitchen designed and has decided he wants two ovens. One is a fan oven and the other is an all in one grill, oven and microwave all in one, one is 2.8 kW and the other is 3 kW. I have run a 6 mm cable to a dp switch above the counter then to a outlet plate behind where the single cooker was meant to go. My first thought was just to run another cabe but now it's been skimmed this would be a pita! Not sure weather to run a new cable and keep them on separate mcb's or to use a dual outlet plate and put them both on the same breaker say a 32a. The cookers are on order so iv no manufacturers instructions at the moment but if I decide to run a new cable I will need to do it before the kitchen fitters come in!! What is the norm when having two ovens as all the new builds I have done up to now have either been a stand alone oven and hob in one or a single oven with a gas hob.

thanks
 
....... or to use a dual outlet plate and put them both on the same breaker say a 32a.

^ That is your answer ^

Any appliance above 13a requires its own supply. These are 2.8Kw and 3Kw so no worries there then. 6mm on a 32A MCB for this install is fine. A dual outlet plate would be needed/best or if you really want to be posh, an Iso switch for each cooker?
 
I despair as to the state of the building industry. Why the hell are plans being drawn after the plasterers have finished? What's the project manager doing to create that royal cockup?

There re is no project manager, it's a local chap who is building on a piece of land he owns so he is running it himself. So it's a kind of make it up as you go alone sort of build witch is a pita as no plans and constant changes etc. Will go there and move the dual output box before next week, thanks all
 
When I was an apprentice my mentor would refuse to start any job like this without a set of plans. And that set of plans was never let out of our custody!

Dave things have change a lot since then. We have to be electrical Ninja's these days! Always ready to react to the ever changing movements of the client/builders requests. End of the day if they dont have a plan, here is the extras bill for your changes!
 
You may find that the all in one grill microwave comes with a 13amp socket attached, did one a while ago, Bosch I thing it was.

The Bosch one that Howdens sell seems to, not sure about the other makes
 
Last edited:
Hmmm, was thinking diversity, but your right of course, looking at the Bosch manual maximum combined load is 2.6kw so it would need to go on the cooker circuit. However, it has a pug attached (with a 16amp fuse apparently!) which manufacturer states must be connected to a socket.
 
Hard to comment without seeing the manual <link?>
Many ovens etc are made for a wide market, europe incl. Sur le continent a usual circuit to the appliance would be a radial with a 16A breaker on it terminating in a 16A socket (schuko is likely).
Note that there is no fuse in the plug, its only us Brits that do these things………..
 
Hmmm, was thinking diversity, but your right of course, looking at the Bosch manual maximum combined load is 2.6kw so it would need to go on the cooker circuit. However, it has a pug attached (with a 16amp fuse apparently!) which manufacturer states must be connected to a socket.


a pug like these?


[ElectriciansForums.net] Two ovens one supply again
 
Still don't have any manual or anything as customer is still deciding on make and model etc, worst case will have to come from outlet plate to two sockets behind each appliance. Not ideal and will have to check if it conforms as will be doing away with the manufacturers plug but it's all boarded so not ideal to have to change the ring main now
 
Still don't have any manual or anything as customer is still deciding on make and model etc, worst case will have to come from outlet plate to two sockets behind each appliance. Not ideal and will have to check if it conforms as will be doing away with the manufacturers plug but it's all boarded so not ideal to have to change the ring main now
Crikey, what is this house powering to require a ring main?!
 
A bit pedantic!:6:

I bet you still say "live" when you should say "line":wink:
I don't think it's pedantic at all. If people in this industry are qualified and working professionally then they should at least be able to use correct terminology to other professionals. Please refer me to where in BS7671 or any of the guidance notes it refers to a 'ring main' and how the phrase used it the above context is correct?
 

Reply to Two ovens one supply again in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
1K
  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
2K
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
582
  • Question
They need to put in a suitable test facility. This should have been part of the design putting in two separate circuits suggests they are not...
Replies
10
Views
3K
  • Question
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...
    • Like
Replies
2
Views
512

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks