You do not need the main earthing conductor for an IR test.
It is a dead test of the existing circuits.
All breakers and main switch on, test from Line tail to earth bar, neutral tail to earth bar, line tail to neutral tail.
Record results
If equipment is installed then it is permissible to join the tails together and test to the earth bar.