Hi, I have 500W, 30A MPPT Charge Controller, 2 x 110ah Leisure Batteries & 1000W 24 V inverter. I want to run a ring circuit of 4 double sockets around my log cabin. Can anybody give me advice on the consumer unit from the inverter and what MCB do I need with instructions. Any photos or drawing wold be great
 
Why do you specifically want a ring circuit, why not just a radial? I'm assuming the sockets are for 230v appliances so you're only going to have a 4Amp supply connected to 4 double sockets, you could just run a radial using 1mm flat twin (depending on length and installation method) and protect it with a 6A MCB.
 
Last edited:
With a 1000watt inverter the maximum current you'll be able to draw will be 4.25 Amps and that's also probably peak load not constant load capabilities. Even a 1mm cable is already probably oversized for the current available, install a 2.5 ring final circuit if you wish but it's a waste of copper and money if the inverter is the only supply you're installing.

The number of sockets you install makes no difference to the amperage available, however many you install you'll have 4.25A total available between them.

What are you planning to plug into this circuit?
 
Entirely your call, the 1kw will probably cover what you've listed but the minute you plug in anything that heats like a kettle or fan heater etc it will trip. Even if you use a 2kw inverter to supply the sockets a 1mm flat twin radial circuit should be fine as long as you're not installing the cable in an insulated wall or something similar.
 
Does the inverter have its own built-in over current protection and On/Off switch? What is the make and model number of the inverter?
 
That's a 1500 watt inverter, I thought you had a 1000w watt version.

It comes with its own built-in overload protection so why install a consumer unit?

This kinda inverter is better used with extension leads as it was intended by the manufacturers. One of the technical issues with this type of inverter in a permanent installation is that the neutral and live usually float with respect to earth, ie there's no internal N-E bond in the inverter so you really should use 2-pole switching if the sockets are switched. Also you have the earthing issues to deal with if you install a CU and hard-wired sockets, you'll need to install an earth rod and bonding if necessary and somehow create a N-E bond on the supply side external to the CU.

Just use extension leads, it's going to save you a lot of headaches.

You say in your profile you're a trainee, is this a job you're doing at someones property?
 
I have considerable experience of generic Chinese inverters. I would seriously consider using eg. Durite or Victron. They cost more but there is a big reason for that. Your biggest fire risk is from a cheap inverter not the wiring.
If you are running CCTV then you may need a bigger battery bank. Check the amps of the recorder (which I guess is AC). If you leave the inverter on 24/7 it will kill your battery. Inverters need to be switched off when not required on small systems. If you know all the loads and have worked out the daily watt hours then you may be OK. However 500watts in winter is not a lot for constant loads after a few days of dull weather the alarm may go off. You have 50% of 110ah of storage for maybe a week of zero solar. Also these cheaper inverters are normally set to switch off the loads when the voltage is 10.5v (x2 for 24v)which is death for a battery. I would get a controller which monitors and controls the loads to cut off before damage is done. Decent MPPT controllers can be programmed to do this with their respective inverters.
 
I've used the Victron inverters and they're good units, not cheap but you get what you pay for. MultiPlus - Victron Energy As Solarfred says the Chinese inverters are something of a lottery, there's a few solid ones but plenty you want to avoid. I'm not sure about other makes and models available in the UK.

To measure the load you should use a test lead and a clamp meter with a 'max hold' facility. If you take the power requirement from the info sticker on the individual appliances it will be highly inaccurate. Make up a test lead like this and use it to actually supply the items.
[ElectriciansForums.net] Off grid Consumer Unit to ring sockets (obviously use a UK 13A plug and trailing socket not the 16A version shown)
 

Reply to Off grid Consumer Unit to ring sockets in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

  • Question
Issue is certain sizes of cable may theoretically be okay but upon the proper testing when it’s commissioned things like a thing may not test out...
Replies
8
Views
1K
  • Question
Why aren't you asking them?
Replies
5
Views
857

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top