Have been doing a Re-wire on a flat. However have come across bit of a problem I could do with a second opinion on.

Basically the tails (16mm twin) going to the 2 floors above are going through the floor boards, then straight up the middle of the bloody bathroom wall :whatchutalkingabout

No protection at all, just 2mm of plaster!

I obviously cannot leave it like this, so what would you guys do? The problem i see is its someone else's supply!

Here is a pic (there used to be a false ceiling):

[ElectriciansForums.net] Upstairs flat tails running through wall issue?


You should be able to see from my drawings where it goes! Still can't believe someone thought it was a good idea :confused5:

Cheers
 
Last edited:
You are in a bit of a quandary there, if the cable is running through the bathroom then it should have 30mA RCD protection!
Options are to sink the cables further into the wall and place steel strip over them, move the cables into the "safe zone" by the corner (not good), leave the cables on the surface (very bad), take the cables to the other side of the wall (into??), cut the cables and deny all knowledge (do not do this).

Really there are very few compliant options at all; perhaps rerunning those supplies elsewhere, that I am sure the house owner would be pleased to pay for!
 
Really there are very few compliant options at all; perhaps rerunning those supplies elsewhere, that I am sure the house owner would be pleased to pay for!

Sounds like the cable is not part of the supply for the owners property. OP says "The problem I see is its someone else's supply!"
 
Hi fella,what is the nature of the origin of this supply,and what earthing arrangements are in place? ...just Richards comment made me think there may be protection in place already...
 
Thanks, the cable accross the ceiling im not "so" worried about as another false ceiling will be going there.

Its the one going up the wall im concerned about! As all it takes is for someone to be fitting a mirror and.....

They are fed from a 60A switch fuse straight from the meters.
Its a TNC-S system. So no Rcd etc.

I have spoken to the chap upstairs who didnt seem too bothered! So he is not going to pay to have it re-directed.

My customer is not keen on paying for it to be re-directed, just wants the cheapest safe solution.
 
I would tell your customer, they have have to resolve this with the owner of the property the tails belong to. It shouldn't be in the situation you've found. There's no easy fix here. Once you start doing anything, you kinda start becoming responsible for the situation. Are the properties rented, do they have landlords?
 
As the discussions go on I would be getting permission off your customer and chopping out the plaster to see how much slack etc and if you can put in place some steel protection it might be as is normally the case that they will not move!
At least you will have a bettter idea of what options are needed !
 
If it's in his property and is not his has no written paper work to say that prior consent has been given for it to be there just remove it and see if the bloke upstairs is no longer that bothered about it, you might get the job of running power to his flat so he can have a cup of tea in the morning
 
If it's in his property and is not his has no written paper work to say that prior consent has been given for it to be there just remove it and see if the bloke upstairs is no longer that bothered about it, you might get the job of running power to his flat so he can have a cup of tea in the morning

The above flat's Water and Gas, if any, will also pass through.
It will be mentioned in both flat's leases.

It looks like the cables were within a cupboard before someone removed it.
Removing the cupboard has increased the risk of damage.
 
Last edited:

Reply to Upstairs flat tails running through wall issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
755
S
  • Article
Unidentified noise in party wall Hi 🙂 Please can anyone help to identify this noise in the wall between me and my neighbour? Complicated but will...
Replies
0
Views
179
shrewmouse
S

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Upstairs flat tails running through wall issue?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top