Hi people.
I was talking to one of the guys at work about taking a wire from the earth on the socket to the metal back box. I know this has been discussed before but I can't find it in a search or in the regs. (must be having an off day).
I remember reading in a thread that as long as the back box has a fixed lug then there is no need for a separate earth but most see it as 'good working practice' to add one.
Clarification is needed. Is a separate earth from the socket to the back box required?
 
You have answered your own question.
Back boxes are defined as an exposed conductive part (not sure why!) and must be earthed, the fixed lugs of a back box are an earth connection and so an earth tail is not required, however it is good practice. If there is no fixed lug then a tail is required.
 
You have answered your own question.
Back boxes are defined as an exposed conductive part (not sure why!) and must be earthed, the fixed lugs of a back box are an earth connection and so an earth tail is not required, however it is good practice. If there is no fixed lug then a tail is required.
Thanks Richard. I thought I'd read it somewhere. Is there something in the BYB or OSG that states this?
 
Last edited:
Thanks Richard. I thought I'd read it somewhere. Is there something in the BYB or OSG that states this?

BS7671 only refers to connecting exposed conductive parts to Earth - it doesn't go into detail about any specific products.

It is dealt with in more detail in the Guidance Notes, which does mention backboxes.
 
543.2.7

The only time you need as per the regulations to fit a fly lead to a back box if the trunking, conduit etc is used as the CPC, and only then.

There is no regulation saying that a back box flush in a wall needs to have a fly lead, if above does not apply. The same as a back box does not need a grommit, but both cases are deemed "best practice"
 
It's in Guidance Note 8.

- 2 fixed lugs: earthing tail is not essential although for best practice is highly desirable.
- 2 adjustable lugs: earthing tail is essential.
- 1 fixed and 1 adjustable: always desirable to provide an earthing tail. Some accessories only have one earthing strap and eyelet, so essential (in this case) that the earthing eyelet is located at the fixed lug position. If not (in other words, if your accessory has only one earthing stap and eyelet, and it lines up with the adjustable lug), then earthing tail is required to be provided.
 
It's in Guidance Note 8.

- 2 fixed lugs: earthing tail is not essential although for best practice is highly desirable.
- 2 adjustable lugs: earthing tail is essential.
- 1 fixed and 1 adjustable: always desirable to provide an earthing tail. Some accessories only have one earthing strap and eyelet, so essential (in this case) that the earthing eyelet is located at the fixed lug position. If not (in other words, if your accessory has only one earthing stap and eyelet, and it lines up with the adjustable lug), then earthing tail is required to be provided.

I haven't the GN 8 to hand, but every guidance note will have the relevant reg to hand next to the note steve, what is that reg number that states the 2 lugs mate
 
That's the weird thing. It doesn't state a reg. It mentions 543.2.7 in the preceding text (which is about providing an earthing tail to the accessory from trunking/conduit where the cpc is provided by the containment). But on the subject of the lugs: nothing.

It starts that section by saying: "A metal back box of a surface-mounted accessory is an exposed-conductive-part [no argument there!], and a metal back box for a flush-mounted accessory is deemed to be an exposed-conductive-part. Back boxes, like all exposed-conductive-parts, are required to be earthed."

In my original post #7 I was pretty much quoting GN8. They are making the point that for 2 fixed lugs "the box can be considered adequately earthed through the earthing straps and eyelets of the accessory."
 
Thanks Steve, not trying to be a smart a*** but please do use the GN notes as they are written, guidance, and unless they quote a regulation then they are pure guidance.

I'm not saying that they are not good guidance but I get really annoyed sometimes with the IET about this. There argument is that anything in the GN notes that are regulations, will have the relevant reg to refer to. All the rest is guidance.

Use them like any tool mate, but it's the BYB that is what we should go to for the regulations
 
Thanks Steve, not trying to be a smart a*** but please do use the GN notes as they are written, guidance, and unless they quote a regulation then they are pure guidance.

I'm not saying that they are not good guidance but I get really annoyed sometimes with the IET about this. There argument is that anything in the GN notes that are regulations, will have the relevant reg to refer to. All the rest is guidance.

Use them like any tool mate, but it's the BYB that is what we should go to for the regulations

Absolutely. I'm sick of seeing quotes from Guidance Notes / On-Site Guide quoted as "Regulations" or "Requirements" - they are an opinion and nothing else. Only BS7671 contains the Wiring Regulations.
 
Thanks Steve, not trying to be a smart a*** but please do use the GN notes as they are written, guidance, and unless they quote a regulation then they are pure guidance.

I'm not saying that they are not good guidance but I get really annoyed sometimes with the IET about this. There argument is that anything in the GN notes that are regulations, will have the relevant reg to refer to. All the rest is guidance.

Use them like any tool mate, but it's the BYB that is what we should go to for the regulations

No argument from me, I'm with you all the way. :)

My original post was aimed at the thread original post, along the lines of, "I'm sure I've seen this somewhere..." well, that somewhere is GN8.

As someone just starting out, the guidance notes are an invaluable source of knowledge, in terms of interpreting the regs and stating what [the IET thinks] is best practice. If you can't cite a source for a statement, it's pretty low value.

They even teach you about this sort of thing on the level 2 course...:

[ElectriciansForums.net] Earthing a back box

It continues... "This will lead to the statutory enforcement system and criminal courts. For example, a breach in the non-statutory IET Wiring Regulations may have a significant effect on safety and ultimately result in a breach in statutory legislation.

Even if a breach in non-statutory regulations is not a legal issue, the consequences can be far-reaching. The industry may lose faith in the offending organisation's ability to perform, resulting in a loss of customers and tenders. In the case of the rules of trade and similar organisations, breaches may result in expulsion from the relevant organisation."

Quoting what someone said on an internet forum (unless they cite a suitable source) is off the bottom of the triangle ;)
 
No argument from me, I'm with you all the way. :)

My original post was aimed at the thread original post, along the lines of, "I'm sure I've seen this somewhere..." well, that somewhere is GN8.

As someone just starting out, the guidance notes are an invaluable source of knowledge, in terms of interpreting the regs and stating what [the IET thinks] is best practice. If you can't cite a source for a statement, it's pretty low value.

They even teach you about this sort of thing on the level 2 course...:

View attachment 30703

It continues... "This will lead to the statutory enforcement system and criminal courts. For example, a breach in the non-statutory IET Wiring Regulations may have a significant effect on safety and ultimately result in a breach in statutory legislation.

Even if a breach in non-statutory regulations is not a legal issue, the consequences can be far-reaching. The industry may lose faith in the offending organisation's ability to perform, resulting in a loss of customers and tenders. In the case of the rules of trade and similar organisations, breaches may result in expulsion from the relevant organisation."

Quoting what someone said on an internet forum (unless they cite a suitable source) is off the bottom of the triangle ;)
it seems questionable how the Regs could hold up in court with Regards to bonding and Earthing when so much of it is so unclear with Hundreds and Hundreds of Questions on bonding and earthing on the Net another hundreds and hundreds in the classroom, surprised someone hasn't considered taking action the other way round.
 
it seems questionable how the Regs could hold up in court with Regards to bonding and Earthing when so much of it so unclear with Hundreds and Hundreds of Questions on bonding and earthing on the Net.

The regulations aren't really very unclear, their language is usually pretty precise.

The biggest problem is people reading the regs who don't understand the correct/proper meaning of the words used, or who have a preconceived idea of what they think should be written there so they try to force what is written to fit their ideas.
 

Reply to Earthing a back box in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
As you said in #9 get an electrician involved. The information you are giving is not clear as you do not understand what is being asked which...
Replies
10
Views
1K
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
618
loz2754
L

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Spoon

Mentor
Nearly Esteemed
Arms
-
Joined
Location
Lancashire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Earthing a back box
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top