Fault finding. Mind boggling | on ElectriciansForums
Guest viewing is limited

Discuss Fault finding. Mind boggling in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 9, 2011
Messages
151
Reaction score
12
Location
Cardiff, but work SW
I'm stumped on this one. My mate has a two way garage board in his garage. Circuit 1 is lighting, circuit 2 is 3 sockets on a radial. Lighting works fine. Sockets trip main RCD in DB when switched on. 3 sockets are now disconnected. Tried to reset 16A MCB (for radial circuit) and still trips RCD. So... Thought, simple, fault is on cable between DB and first socket. Disconnects live from out of top of MCB and it stays on. But.... When I push cable into top of MCB again, (even though the MCB is switched off), the lights go out (but don't trip) and arc like crazy from the bottom of the MCB). Bearing in mind this cable goes from the DB to the first socket and is disconnected at both ends!! Only things I haven't done is disconnect the neutral as well whilst trying to connect it back in. I realise this is an absolute headache to read. But if you manage to understand, could you give your opinions. Much appreciated, Lee
 
I suspect people will want to know what test results you have got - assuming you haven't just done the 'keep switching it on' method :) Daz
 
The lights stop working you say, is that without the B6 or RCD tripping? Where is it arcing from? Could possibly be the busbar is not in the cage clamps properly or tightened. I have had that tripping out seemingly random circuits before. But if the B16 is off when you try to connect the live in to it, that suggests a neutral fault maybe. Thinking out aloud here so may be off track!

Have you tried a different breaker? Or checked for continuity on the existing one and that you get open cct when it's off.
 
Last edited:
If there's arcing from the bottom of the MCB then there is a bad connection there - can't be an arc if there is a good solid connection made. I would take both MCBs out and all cables (including neutrals) and connect everything up fresh. IR test of all cables including neutrals as well. Daz
 
The lights stop working you say, is that without the B6 or RCD tripping? Where is it arcing from? Could possibly be the busbar is not in the cage clamps properly or tightened. I have had that tripping out seemingly random circuits before. But if the B16 is off when you try to connect the live in to it, that suggests a neutral fault maybe. Thinking out aloud here so may be off track!

Have you tried a different breaker? Or checked for continuity on the existing one and that you get open cct when it's off.

yes that's correct. The 6A MCB doesn't trip which would suggest to me the problem is on the incoming side of the breaker. ie, loose connection on busbar. Will try securing connections now and report back. Lee
 
If making a connection to the 16A MCB when off causes the RCD to trip, either it's not really off (unlikely) or the trip resulted from something else being disturbed. You can confirm that the MCB is really opening with an insulation tester, then move on to find what is being disturbed.

A golden rule of fault finding is never to let your mind boggle! There's usually a very simple explanation for everything, which you will invariably find if you break a system down into small parts that can be conclusively proven to be, or not to be, part of the problem. E.g., something that arcs (other than a welder!) is either a poor connection or contact. You've got that symptom so find the cause, never mind RCD tripping or not tripping or whatever, find the cause of the arcing (probably busbar not properly located). Once you've done that, move on to the next bit. etc.
 
As I said earlier and others have also said check the busbar. I would remove the din rail wholesale with RCD and MCBs attached still and check that the busbar is correctly located in all three cage clamps. As I said loose connections can cause RCD to trip. Are there any signs of heat damage to the MCBs or RCD.
 
Last edited:
Give your mate the Spanish Inquisition as well. I've been lead on a merry dance, by customers not telling the full 'story'.

Yeah, annoys me that one. I often ask whether they have done something they don't don't want to mention for fear of looking stupid! I say I may find the problem much much quicker (and cheaper) if they tell me the truth, the whole truth and nothing but the truth! The prospect of it being cheaper normally entices them to swallow their pride!
 
Are there any signs of heat damage to the MCBs or RCD.

This was a recent weekend callout. House is about 15 years old, with no significant modifications, so I recon the busbar was installed like this from new.

Note that this is not high current stuff. All the breakers on the affected busbar are 6A. Two alarms and three lighting circuits. Quite surprised at how the busbar has been eroded away. Somewhat amazed that the occupants had only recently noticed anything wrong.

[ElectriciansForums.net] Fault finding. Mind boggling
[ElectriciansForums.net] Fault finding. Mind boggling
[ElectriciansForums.net] Fault finding. Mind boggling
[ElectriciansForums.net] Fault finding. Mind boggling
[ElectriciansForums.net] Fault finding. Mind boggling
 
One thing you have to watch out for is the Wylex NSB breakers and also the equivalent crabtree and the Steeple breakers too , these were all subject to the Electrium recall and breakers should have been checked and sticker fixed on the board , I did quite a few of the recall visits and replaced loads of breakers , but I notice on many call outs with this problem that theres loads out there that didn't get replaced , where sparks have accounts at the wholesalers the use of these boards could be chased , but theres loads that had been bought for cash etc that hadn't ........
 

Reply to Fault finding. Mind boggling in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
792
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
610
davesparks
D

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Cardiff, but work SW

Thread Information

Title
Fault finding. Mind boggling
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top