Dave OCD

-
Mentor
Esteemed
Arms
Joined
May 5, 2015
Messages
4,158
Reaction score
6,674
Location
Cornwall
I have an extension to wire this week which is a garage conversion comprising a study, shower room and small store area. The supply is TT and I'm intending on running a 16mm sub main from the existing mains position under the suspended floor through the hall in the house and installing a new small CU with RCBOs in the new store area. Due to the earthing arrangements I'll fit an S type 100ma RCD and 60a Switch-fuse [possibly 63a MCB] at the supply end, either seperate units linked by tails or integrated in one unit if I can source something suitable. Do you think these items should be Amendment 3 compliant as I don't think I've seen such a beast yet ? Any pointers to similar recently used kit would be welcome. :smilewinkgrin:
 
Is it an actually requirement that the door is hinged to shut itself? Just think if you had to install a 3phase board within a domestic property if this was the case.

No,it's not a specific requirement....but for me that is not complying with the intention of the regulation which is a fire resistant enclosure over all 'combustible' components as far as is practical. That is why all Am 3 designed enclosures I've seen have a top hinged metal lid. I wouldn't fit that wylex unit. I take your point about the 3 phase board,but that would easily be overcome by fitting 3 separate single phase DB's if you took the view that a side hinged door was not compliant. I would take that view as the door left open would negate any fire resistance of exposed 'combustible' components.
 
Last edited by a moderator:
The hinged lid is a good idea but I've already seen a board installed where the wall was out and the lid ever so slightly stayed open. Imo a catch or similar is better. Edit: What switch fuse would you install? As there doesn't appear to be many on the market atm that meet the requirements.
 
Last edited:
What brand of RCBOs you using in the new CU.? Always found DP versions tricky to get

That's a good point, as you've rightly noticed I'm talking about a TT install. I might even go with a small dual RCD board if this proves problematic although single pole switched neutral RCBOs would comply. All a bit OTT when there will be DP isolation upstream and the sockets will all be DP as well as the shower isolator.
 
anyone ever managed to set one of these on fire? i've tried with a blowtorch. it just chars. will not ignite, ergo it's non-combustible. it's a totally different type of plastic to the crap they make CUs from.

[ElectriciansForums.net] Opinions please.
 
anyone ever managed to set one of these on fire? i've tried with a blowtorch. it just chars. will not ignite, ergo it's non-combustible. it's a totally different type of plastic to the crap they make CUs from.

View attachment 31427

That's what I'd like to use on this job and I know it would be perfectly safe. :mad2:
 
then use it then. only thing with them is they're designed for incomer at bottom, out at top. can fuse at 40,60,80 or 100A.

ewdit: and the switch is down for ON.
 
I used one of these recently on a job. Tails in the top using Wago sprint glands in one knockout. 16mm SWA glanded at the bottom. Comes with 3 fuses and mine had a metal hinged door on it rather than the plastic in the picture.

https://www.tlc-direct.co.uk/Products/CGFS100.html



Only downside is it is a bit big if your tight for space.

That could be ideal, could even put the S type RCD in that instead of the 100a DP switch , tin hat on now. :grin:
 
my understanding of the new regulation is that only domestic consumer units and "similar switchgear containing OPD's" need to be of a non combustable construction.

a standalone rcd has a completely different British standard / product definition to a c.u. therefore would fall outside the requirement and a pvc enclosure could be continued to be used.

to put it another way , you may find that on a TT arrangement the dno may prefer or even insist on double insulated upfront isolating / rcd enclosures for obvious safety reasons.
 
Last edited by a moderator:
my understanding of the new regulation is that only domestic consumer units and "similar switchgear containing OPD's" need to be of a non combustable construction.

a standalone rcd has a completely different British standard / product definition to a c.u. therefore would fall outside the requirement and a pvc enclosure could be continued to be used.

to put it another way , you may find that on a TT arrangement the dno may prefer or even insist on double insulated upfront isolating / rcd enclosures for obvious safety reasons.

Where did you get the 'containing opds' bit from? It doesn't say that in the regs.

A standalone RCD in a 2way enclosure is very similar switchgear to a CU.

Why would the DNO give a monkeys? After their terminals they really don't worry too much unless your tails are too long or you damage their network somehow
 
Where did you get the 'containing opds' bit from? It doesn't say that in the regs.

A standalone RCD in a 2way enclosure is very similar switchgear to a CU.

Why would the DNO give a monkeys? After their terminals they really don't worry too much unless your tails are too long or you damage their network somehow

The RCD will be going in the same Amd 3 Compliant enclosure as the cartridge fuse, the RCD will take the place of the usual DP switch [100a rated 100ma time delayed] so I'm covered and it'll be a nice tidy solution. :smile:
 

Reply to Opinions please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
If it is unused it could be capped close to ground and covered with insulation at the main building. I.e. Opposite to first thought of bonding at...
2 3
Replies
52
Views
7K
  • Question
I think you should have started a new thread. Although similar question, the situations are different and answers are now going to be confusing.
Replies
21
Views
11K
Hi @NorthEastSpark, we supply Lewden via our online store. As a forum member you can also get an extra 5% discount. Just sign up for an account...
Replies
13
Views
2K
  • Question
Good questions - I forgot to write that down. The white route is not exceeding 275m including drops. We need about 20A per phase peak demand in...
Replies
12
Views
3K
  • Question
Option 2 but RCBO board.
Replies
6
Views
1K
Octopus
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks