Hi,

Just wandering what to use to get an armoured through a new duct which has been installed prior to me being on site without a pull rope.
Longest run is about 30 meters with probably 2 bends and is about 3 inch diameter but is the flexible type with ridges.
Will rods go that far and round bends especially with it being the ridged type of duct?
I have seen the continuous rod on a reel that bt etc use, is this my only option to hire one and are they flexible enough etc to go round bends of this size etc?

Thanks
 
30 meters is pushing your luck especially with corrugated wall ducting. You could try but you'd need to use an end attachment that looks like an egg whisk.

[ElectriciansForums.net] cable ducting without pulling rope installed
 
What you need is a VERY strong vacuum, some light string, a mate to let it out and a load of patience - I've done it, then pulled through a heavier string, before move on to the cable, HOWEVER in your case the bends and length may make it a no,no!
 
Something that's worked for us on more than one occasion is using two sets of rods, one from each end. On one side you use the egg whisk attachment and on the other you have a hook. The theory being when they meet in the middle the rod from one side hooks onto the rod from the other side.
 
I have had the same issues before and with several bends , I tried all sorts with no success , I was told about a pump tape and it worked really well , that was back in the 80s on riser renewals in blocks of flats over long distances too..
 
What you need is a VERY strong vacuum, some light string, a mate to let it out and a load of patience - I've done it, then pulled through a heavier string, before move on to the cable, HOWEVER in your case the bends and length may make it a no,no!

Seen a video on social media lately with a guy using the same method but using an inflated condom as a lead bung tied to the string to fill the duct up for maximum suction.
 

Reply to cable ducting without pulling rope installed in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top