9.5 kW shower on 2.5!!! | on ElectriciansForums

Discuss 9.5 kW shower on 2.5!!! in the Talk Electrician area at ElectriciansForums.net

Joined
Nov 7, 2012
Messages
107
Reaction score
52
Location
Newcastle
I was doing a eicr today. Came across a shower 9.5 kW Mira ,which had been installed for at least 8years.
its was brutally spurred off the bathroom heater which was protected by a 15'amp rewireable fuse. All, done in 2.5 t&e .
The client swore he knew nothing about it, and said he did have someone change the shower a good few years ago .
He also claimed it had never blown the fuse , I checked it was 15 amp wire , and I can only assume on cold days the heater was on as well and the shower was working hard.
Bizarre
To be fair the cable was still in good condition and belled out at 299.
whats going on here folks. It dosent add up!!
 
I saw one once connected to the upstairs lighting circuit with a 30a wire in the 5a 3036 fuse. The 1.0mm cable had completely melted where it passed through insulation,but was visually undamaged in free air. It was chased into the wall on the drop to the CU and the heat damaged several of the cables chased in alongside it.
Householder had only just moved in....lovely surprise for them!
 
I was doing a eicr today. Came across a shower 9.5 kW Mira ,which had been installed for at least 8years.
its was brutally spurred off the bathroom heater which was protected by a 15'amp rewireable fuse. All, done in 2.5 t&e .
The client swore he knew nothing about it, and said he did have someone change the shower a good few years ago .
He also claimed it had never blown the fuse , I checked it was 15 amp wire , and I can only assume on cold days the heater was on as well and the shower was working hard.
Bizarre
To be fair the cable was still in good condition and belled out at 299.
whats going on here folks. It dosent add up!!


Belled out? whats that
 
It's more commonly used to refer to a continuity test Pete, even more odd.

I realise what it means but as an Apprentice he should be taught to use the right terminology "belled out at 299" what apples sorry Ive got a headache and that sort of thing really ticks me off.
 
I realise what it means but as an Apprentice he should be taught to use the right terminology "belled out at 299" what apples sorry Ive got a headache and that sort of thing really ticks me off.
too mmuch of the red?
 
I realise what it means but as an Apprentice he should be taught to use the right terminology "belled out at 299" what apples sorry Ive got a headache and that sort of thing really ticks me off.
I'm really sorry my terminology annoyed you so much, consider me well told off and I will stand in the corner for 20 mins.
Its a common terminology up my way. I assume it comes from the old testers which basically were an audible continuity.
i applied 500 volts to the cable and it gave me a reading of greater than 299 ohms. Hope that helps.
 
I'm really sorry my terminology annoyed you so much, consider me well told off and I will stand in the corner for 20 mins.
Its a common terminology up my way. I assume it comes from the old testers which basically were an audible continuity.
i applied 500 volts to the cable and it gave me a reading of greater than 299 ohms. Hope that helps.


299 Mohms you mean, Don't forget the dunces cap, and you have detention for the next week
 
I'm really sorry my terminology annoyed you so much, consider me well told off and I will stand in the corner for 20 mins.

I hope you realise that you have to go in 'the naughty corner' 1 min x age. So unless you are 20 years old then the time needs altering..... :)
 
Most showers have 2 power settings, maybe its always on the first one.
 
Come on guys, give the guy a break, we were all apprentices once. So he got the terminology wrong, none of us a perfect, but at least he had the balls to come on here and ask the question.

I'm being a good boy..... Then again I always am.... :)
 
Come on guys, give the guy a break, we were all apprentices once. So he got the terminology wrong, none of us a perfect, but at least he had the balls to come on here and ask the question.

Pretty sure Pete and the guys were having a larf, and pretty sure the OP took it as such given his response. All in good spirit I reckon.
 
Now if someone said they had 'belled something out at 299' I would think 299 ohms, not 299 megohms, because 'bell test' is slang for continuity test not insulation. So here it was definitely the wrong term especially as the units weren't given although I don't mind the phrase 'bell out' used in the right place. Much like saying you 'paced out the length at 25' which would imply yards, but actually you meant measured with a rule at 25mm.
 
I'm not offended. Trust me, I have bigger things to worry about at present than someone having a dig at me on tinternet
Also , I ain't an apprentice, ( unfortunately) don't know where that came from. Every day's a school day though and there's lots I don't know. And my terminology was very poor , bad habits I suppose. Apologies again to the grammar police :party3:
 

Reply to 9.5 kW shower on 2.5!!! in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
SparkyChick covered that in her comprehensive reply above.
Replies
8
Views
4K
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
587
  • Question
Thanks indeed, Lucien, RE THE ABOVE If each coil has one of the three phase connected to it, and a delta configuration has only three supply...
2
Replies
25
Views
7K
L
  • Question
Being a Proteus it probably wont make much difference :-)
    • Like
Replies
22
Views
7K
  • Question
Hi guys thank you very much for all your replies So am I right in saying that regarding installing the shower there are two possibilities? One...
Replies
17
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks