I'm back on the tools. What the hell is wrong with these testing companies? | on ElectriciansForums

Discuss I'm back on the tools. What the hell is wrong with these testing companies? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Sparky Ninja

-
Mentor
Arms
Joined
Aug 18, 2009
Messages
2,890
Reaction score
881
Location
North East
Well I'm am out of the training game for a bit..

I've got a couple of work offers but I am basically whoring myself out to whatever is paying for the foreseeable..

So I've done a full test of a primary school this week, I was handed Amtech Fastest loaded on a laptop which had all the cert data pre-loaded from someone else and I was asked to just test and fill in the blanks.


So a couple of things (bearing in mind the extent claimed 100%):

1 - Since when was it ok to 'tick' the R1&R2 having just carried out a Zs?
2 - Oh and regarding that Zs, don't look for the highest, or work out the furthest. Take it from the lowest ceiling.
3 - Since when was it acceptable to not even attempt to do IR?
4 - "Pump room? we don't go in here we just LIM it"


I've just completed a school for this company and have data they don't want because they have never had so much and don't need it.. or maybe know what it is?
I've measured current imbalances, taken thermal images and done power quality analysis on their BMS main control panels.

Oh and all the 'electrically competent person' observations I have made - that granted are not non-compliance's with BS 7671 but are non compliance's with BS 5266, The IET PAT CoP and BS 7909 to name a couple. They don't want to pass them to the customer either - probably because they don't understand them..



Basically I was given a week in the building so did everything I could in the time given. It was all tested by Thursday which left me with a day to go round double checking and carrying out inspections - but the 'QS' has chosen to change my IR readings back to LIM and my measured values of R1&R2 to 'ticks'..

What a douche!

Oh and Amtech Fastest software? What a restricting auto adjusting load of crap.




If testing companies are going to treat the testing work this way it's going to end up like PAT.



Oh, and one of the observations I made.. see if you can spot it.

[ElectriciansForums.net] I'm back on the tools. What the hell is wrong with these testing companies?

[ElectriciansForums.net] I'm back on the tools. What the hell is wrong with these testing companies?
 
Sounds like the usual rubbish testing being reported even when the inspection and testing has been done correctly!
They cannot up their game or it would make the other bodgers look bad!
No idea about Amtech, surely it is easier to use , no more of this writing down figures, icons and symbols are much easier.:stuart:

Observations on the panel, random loose white cable taped over?
Change of phase sequence from isolator?
 
I would guess but hard to tell from a photo.. are those data cables thus where they are bared back they are not rated to the cables they share in the same trunking?
Also insulating stabs on the empty outputs seem to be for decoration as there are isolating switches for the busbar stabs.
Last be not least, the whole MCB section is upside down, now that might cause the electic to flow the wrong way :mellow:...unless your photo is inverted?
 
Last edited by a moderator:
Well I'm am out of the training game for a bit..

I've got a couple of work offers but I am basically whoring myself out to whatever is paying for the foreseeable..

So I've done a full test of a primary school this week, I was handed Amtech Fastest loaded on a laptop which had all the cert data pre-loaded from someone else and I was asked to just test and fill in the blanks.


So a couple of things (bearing in mind the extent claimed 100%):

1 - Since when was it ok to 'tick' the R1&R2 having just carried out a Zs?
2 - Oh and regarding that Zs, don't look for the highest, or work out the furthest. Take it from the lowest ceiling.
3 - Since when was it acceptable to not even attempt to do IR?
4 - "Pump room? we don't go in here we just LIM it"


I've just completed a school for this company and have data they don't want because they have never had so much and don't need it.. or maybe know what it is?
I've measured current imbalances, taken thermal images and done power quality analysis on their BMS main control panels.

Oh and all the 'electrically competent person' observations I have made - that granted are not non-compliance's with BS 7671 but are non compliance's with BS 5266, The IET PAT CoP and BS 7909 to name a couple. They don't want to pass them to the customer either - probably because they don't understand them..



Basically I was given a week in the building so did everything I could in the time given. It was all tested by Thursday which left me with a day to go round double checking and carrying out inspections - but the 'QS' has chosen to change my IR readings back to LIM and my measured values of R1&R2 to 'ticks'..

What a douche!

Oh and Amtech Fastest software? What a restricting auto adjusting load of crap.




If testing companies are going to treat the testing work this way it's going to end up like PAT.



Oh, and one of the observations I made.. see if you can spot it.

View attachment 32365

Is that panel CE marked?
 
Not sure what that SP+N is doing at the top right. There's no main MCB and it looks like a t/pole isolator toward the bottom right.
 
Triple pole breaker in wrong position involving 2ways.....G, Br, Bl ?....and Merlin
 
I work for a testing company and are constantly out priced by companies who promise the world and fail to deliver, the client is generally none the wiser. Is it that the distribution board is full of non compatible protective devices.
 
An "oh dear" moment just now when looking at the pic. I am seeing data cables in here - these go out to the PCs the kids touch - please someone tell me I'm wrong? Not to mention the IT tech who bumbles about with these cables from time to time. I bet they've no idea about live working or how to make safe. I hope I am wrong :)
 
I'm back on the tools for summer. Was taken on by a large contractor and given to someone who would "show me the ropes"

He happened to be someone who I trained and assessed his 2391 practical. I was stringent about meeting all the criteria and completing results accurately.

He measures the Ze, a Zs on one socket per ring and the RCD. That's it. 10 minutes of testing then 30 minutes of fudging the rest on a tablet. Up to eight installations a day.

All the time teaching and training the guy about the importance of the job and a few years later he's a sticker jockey.
 
I'm back on the tools for summer. Was taken on by a large contractor and given to someone who would "show me the ropes"

He happened to be someone who I trained and assessed his 2391 practical. I was stringent about meeting all the criteria and completing results accurately.

He measures the Ze, a Zs on one socket per ring and the RCD. That's it. 10 minutes of testing then 30 minutes of fudging the rest on a tablet. Up to eight installations a day.

All the time teaching and training the guy about the importance of the job and a few years later he's a sticker jockey.
Is this actually serious.
 
From what I've seen most of these testing firms are a complete joke....Pittance per circuit, no real inspection and made up test results. Most customers don't care as long as they get a satisfactory report for a cheap price.
 
From what I've seen most of these testing firms are a complete joke....Pittance per circuit, no real inspection and made up test results. Most customers don't care as long as they get a satisfactory report for a cheap price.
I agree but this post doesn't read correct, he says he trained this bloke, did he say nothing.
 

Reply to I'm back on the tools. What the hell is wrong with these testing companies? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top