So I've done a full test of a primary school this week, I was handed Amtech Fastest loaded on a laptop which had all the cert data pre-loaded from someone else and I was asked to just test and fill in the blanks.
So a couple of things (bearing in mind the extent claimed 100%):
1 - Since when was it ok to 'tick' the R1&R2 having just carried out a Zs?
2 - Oh and regarding that Zs, don't look for the highest, or work out the furthest. Take it from the lowest ceiling.
3 - Since when was it acceptable to not even attempt to do IR?
4 - "Pump room? we don't go in here we just LIM it"
I've just completed a school for this company and have data they don't want because they have never had so much and don't need it.. or maybe know what it is?
I've measured current imbalances, taken thermal images and done power quality analysis on their BMS main control panels.
Oh and all the 'electrically competent person' observations I have made - that granted are not non-compliance's with BS 7671 but are non compliance's with BS 5266, The IET PAT CoP and BS 7909 to name a couple. They don't want to pass them to the customer either - probably because they don't understand them..
Basically I was given a week in the building so did everything I could in the time given. It was all tested by Thursday which left me with a day to go round double checking and carrying out inspections - but the 'QS' has chosen to change my IR readings back to LIM and my measured values of R1&R2 to 'ticks'..
What a douche!
Oh and Amtech Fastest software? What a restricting auto adjusting load of crap.
If testing companies are going to treat the testing work this way it's going to end up like PAT.
Oh, and one of the observations I made.. see if you can spot it.
I've got a couple of work offers but I am basically whoring myself out to whatever is paying for the foreseeable..
So I've done a full test of a primary school this week, I was handed Amtech Fastest loaded on a laptop which had all the cert data pre-loaded from someone else and I was asked to just test and fill in the blanks.
So a couple of things (bearing in mind the extent claimed 100%):
1 - Since when was it ok to 'tick' the R1&R2 having just carried out a Zs?
2 - Oh and regarding that Zs, don't look for the highest, or work out the furthest. Take it from the lowest ceiling.
3 - Since when was it acceptable to not even attempt to do IR?
4 - "Pump room? we don't go in here we just LIM it"
I've just completed a school for this company and have data they don't want because they have never had so much and don't need it.. or maybe know what it is?
I've measured current imbalances, taken thermal images and done power quality analysis on their BMS main control panels.
Oh and all the 'electrically competent person' observations I have made - that granted are not non-compliance's with BS 7671 but are non compliance's with BS 5266, The IET PAT CoP and BS 7909 to name a couple. They don't want to pass them to the customer either - probably because they don't understand them..
Basically I was given a week in the building so did everything I could in the time given. It was all tested by Thursday which left me with a day to go round double checking and carrying out inspections - but the 'QS' has chosen to change my IR readings back to LIM and my measured values of R1&R2 to 'ticks'..
What a douche!
Oh and Amtech Fastest software? What a restricting auto adjusting load of crap.
If testing companies are going to treat the testing work this way it's going to end up like PAT.
Oh, and one of the observations I made.. see if you can spot it.