Hi all,
Page 66 Table 7.1 in OSG for 30A BS3036 4.0/1.5mm says "NP" and "Npol" (combinations not allowed in any of the installation conditions)... can someone confirm this please?
Reason is I'm preping for inspection and testing course and reading Chris Kitcher's Practical Guide to I.T and Cert' book, and one of the scenarios is as follows:
new ring consisting seven sockets, 53 metres of 4.0/1.5mm t&e protected by 30A BS3036 fuse, TNCS, 100A main BS1361 fuse, 100A BSEN 61008-1 RCD as main switch.
Hypothetical, but is this allowed in practice as OSG seems to suggest not?