If the switch is open the carrier will be de-energised. If the switch is closed it will be energised.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Gridswitch fuse spur? in the Electrical Tools and Products area at ElectriciansForums.net
...open?
If the switch is open the
Sorry...misread. Maybe 'because the switch is open' would have read easier :lipsrsealed2:
The fuse is put in series after the switch for the reasons Risteard has said. That's why switched fused spurs are constructed in same way.No you feed to your fuse then from your fuse to the switch and then from the switch to the load. so in an 8way grid you could have 4 outgoing loads
Yes i do agree with you . I did write my post that way first then edited it to read the otherway around after seeing richards drawing for continuity as i felt it does not make much difference , I agree with you that industrial switched fuses are wired this way otherwise you could touch a live part of the fuse even when tured off. but with the type of fuse holders we are talking about there is no way of touching the live part of the fuse when inserting it, saying all that going to the switch first is the better way of doing itThe fuse is put in series after the switch for the reasons Risteard has said. That's why switched fused spurs are constructed in same way.
I would have to say the fuse after switch scenario is probably safest but I could not be bothered to change the diagram, FCU carriers are designed to be safe to insert fuses even when energised as they are for unskilled use but no sense in increasing risk.
wire like this in that case.
View attachment 32430
Like an dedicated RFC just for the grid?. Yep like that design.At the risk of sounding pedantic you've drawn the supply as a radial, ie to be able to use a 32A OCPD you'd need to terminate 2 x 4mm² wires in each terminal, except in the last, and then you need to get all the wires in the backbox to screw back the faceplate.
I don't think you'd get very far wiring it in a 2.5mm² radial - you might be OK running a gas hob, extractor and possibly fridge freezer, but you might be in trouble if the compressor were to kick in while the washer dryer were running, especially if the customer had set it and gone out for the day expecting to come home to clean dry clothes but instead found a washer dryer full of clothes and water and a freezer full of food and water.
IMO it would be easier to wire this in a 2.5mm² ring to be able to draw the 32A.
Reply to Gridswitch fuse spur? in the Electrical Tools and Products area at ElectriciansForums.net
Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.