I understand how to test Ze and Zs and that Zs is the total impedance from the suppliers tranny to the final accessory in a circuit your testing. Also that Ze is the suppliers earth resistance.

However i have a few questions

1.) how does the test meter actually work to measure Ze by connecting the meter to the main earth (obviously main earth disconnected from MET) and to the phase conductor? does it link it out or send a current or what?

2.) Why and how does Zs effect a devices tripping time? like what is the theory behind it. I know Low Zs means that fault current will be higher thus tripping the device but how does it trip the device and what device MCB ? RCD? how does fault current going down earth trip a MCB?

3.) Would you be able to just do a test from the main isolator in the disboard and record that measurement for all the Zs readings (adding Ze reading off course) on different circuits or does it have to be done individually for each circuit to get the furthest point in the circuit?

4.)Does the meter measure prospective fault current by just using ohms law and dividing mains voltage by resistance of the cable but what i dont understand is how does the meter find the resistance of the cable does it pull a load on it and then calculate or what?


Thank you for your time
 
A few points Zs and ze are different reading , if you test at the mains as you say that will be ze ,you could link out a light (l-e)and test at the board but this would be a r1+r2 test witch is done dead not live . Efli testers don't trip mcbs they can trip rcds ,
 
basically your meter can only measure one thing.i.e.current. depending on what setting you are using, this current is converted by the meter into volts or ohms . think about a dead resistance measurement. the meter applies a voltage to the circuit (from it's batteries) and measures the current. this is translated into ohms by the mater using ohms law through it's internal electronics. when measuring Ze and Zs, the voltage is derived from the supply, not from the meter. this is why a separate EFLI tester does not have batteries.
 
here:

[ElectriciansForums.net] Zs, Ze how the tester works?
 
Mcbs work on thermal and magnetic principles. Magnetic for sudden rush of current like a short circuit which the thermal side will not sense quick enough. The thermal side is for overcurrent. The fault path will send current down the earth and line conductors and it is the line current which activates the device. Unless a device is faulty it is current only which activates a device or fuse.
 
I am still quite confused on why loop impedance has anything to do with how quick a protective device would trip? i just dont understand how earth has anything to do with a mcb tripping in short circuit conditions or the RCD tripping in earth fault conditions surely the RCD will see the difference in current regardless of the earth being high impedance or not?
 
A few points Zs and ze are different reading , if you test at the mains as you say that will be ze ,you could link out a light (l-e)and test at the board but this would be a r1+r2 test witch is done dead not live . Efli testers don't trip mcbs they can trip rcds ,
what confuses me is when i am always told Zs = Ze (R1+R2). so does that mean R1 and R2 is measured for each individual circuit by being cross connected then the ze measurement is added on that by the person testing to give Zs? so Zs is basically just R1 and R2 cross connected plus the Ze reading?

Its because i saw a video earlier showing a person testing Zs from a scoket outlet. but surely you can just test it like that because you would have to add the Ze reading?
 
what confuses me is when i am always told Zs = Ze (R1+R2). so does that mean R1 and R2 is measured for each individual circuit by being cross connected then the ze measurement is added on that by the tester to give Zs? so Zs is basically just R1 and R2 cross connected plus the Ze reading?
Meter sends a current 25amps through live and earth when meAsuring ze and records the volt drop and converts to ohms on the meter.
 
but why do you need to put a probe on the earth and the line conductor? does the meter short them out or something?
Hope not, there'd be a Big Bang :)
If we want to measure the resistance between two points we need to apply the test to those two points. Zs is between line and protective conductor, so leads are attached to line and protective conductor. Check 411.4.5 for definition. In terms of the meter that takes the measurement, it is a bit special as the circuit is live and in service. Not your average multimeter set on low Ohms range :)
 
Hope not, there'd be a Big Bang :)
If we want to measure the resistance between two points we need to apply the test to those two points. Zs is between line and protective conductor, so leads are attached to line and protective conductor. Check 411.4.5 for definition. In terms of the meter that makes is measurement, it is a bit special as the circuit is live and in service while the meter is taking this measurement. Not your average multimeter set on low Ohms range :)
but this is the concept i am struggling with you cannot measure the resistance of one piece of wire unless you have long leads either end or unless of course you cross connect and measure at end point?! thats why i am wondering how the meter does it for Ze
 
Understand the principles of circuit protection and don't lose too much sleep over the operation of an earth fault loop impedance tester, I commend you for wanting to know but it is clouding over what you NEED to know. Trust me it doesn't matter how it works.
 
but how can it record the volt drop when your not at the other end of the cable to measure the volt drop!!! does it magically go around the live and back through the earth?
In simple terms, the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor as A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument by dividing supply voltage by the value of this current. The resistance of the added resistor must be subtracted from this calculated value before the result is displayed. An alternative method is to measure the supply voltage both before and whilst the loop current is flowing. The difference is the volt drop in the loop due to the current, and loop impedance is calculated from voltage difference divided by current.
 
In simple terms, the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor as A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument by dividing supply voltage by the value of this current. The resistance of the added resistor must be subtracted from this calculated value before the result is displayed. An alternative method is to measure the supply voltage both before and whilst the loop current is flowing. The difference is the volt drop in the loop due to the current, and loop impedance is calculated from voltage difference divided by current.
THANK YOU!! now that has made a switch flick in my head, just a one more thing if you can how does Zs effect the tripping time of a MCB or RCD?
 

Reply to Zs, Ze how the tester works? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
Replies
7
Views
520
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
563
loz2754
L
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Replies
21
Views
1K
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
773
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks