Draw it out Steve, the N>E link is before the RCD, so current flowing down the PE will not go through the RCD causing an imbalance.
Sorry South Spark for meandering off a bit...Ok long day so bear with me. Informative video but it seems to me that it only applies if there is no other path to earth than the affected person.
If the PEN is broken then would the current not flow back through the bonding to true earth especially if I introduce earth rods into the system?
Could I introduce an earth rod connected to the earth terminal in the socket?
Utilise the Pme for the socket,add a rod
Don't employ any Horses,Donkeys or Cows to operate the sound system and every ones happy
Just checking, that you agree an RCD will not afford additional protection, in the case of a broken PEN conduct?Draw it out Steve, the N>E link is before the RCD, so current flowing down the PE will not go through the RCD causing an imbalance.
Is there a way forward with this situation ..... in the case of a broken PEN conduct?
Just checking, that you agree an RCD will not afford additional protection, in the case of a broken PEN conduct?
Not without the addition of a local earth rod connected to the met.