Working on a old property in a slightly remote area installing a new circuit.

When I looked at the earthing it looked like a tns but I investigated and found a old 2.5mm running towards the rod.

My problem is I am getting a ze reading of 0.25 ohms.

Ino we had a really heavy down poor the day before but to be that low?

I am wait for the dno to confirm the earthing but they ain't rushing.

Any thoughts
I know a good reading for tt is 200 ohms or lower. This is the first one I have worked on
 
I think you are right to be concerned as there will always be risks banging in a rod. As we spend a bit of time looking at the existing bonding, I have a go at estimating where I think the services would run from that, look of water connection at property boundary etc. I speak to owner and get their take on where services may be. If I've any doubt remaining, I dig a bit by hand which is the only thing that saved me in the attached pic. The cost of ground penetrating radar hire is £300 or so per day, and probably be about the same if you get a specialist company to do a report on a domestic plot. Folks won't pay for that to have a new circuit in their house, but it's the only way to be sure about what's below.

[ElectriciansForums.net] Earth arrangements confusion
 
I try and opt to locate spike to the rear of a property to avoid any services (here they're always brought from the road/street to the front of a property) and assess drainage and guttering on a property so as to avoid any drainage pipes.

If frontal location was only option and I wasn't 99% certain I was safe to put a spike down I'd likely have to get further assessment done as whilst a cable finder will locate telephone, virgin and mains etc, water and gas pipes are ran in pvc pipe. So would not show up on any scanner that I've seen.
Although in general the services are brought the most direct route from street to gas metering equipment/internal stop cock. But not always. Although it's very rare to find them travelling an indirect route here.
Fortunately it's very rare for me to find TT properties here with no spike already installed, so it's not actually something I have to do very often. That was first this year and only did 2 last year and 1 of those was a new build property in the countryside where all services were visible.

But common sense and a basic knowledge of how services are routed to properties helps decide.
 
Thanks for the replies chaps, that was a close en Wiko. My son's having an extension done. When they were digging the footings, they found some unexpected drainage pipes. Thames Water came out and camera'd them, and found another waste pipe. Both were 3' feet down, and if I'd look for a place to put a rod, I'd hit both!

If this 18th proposal goes ahead, it might prove expensive.
 
Thanks for the replies chaps, that was a close en Wiko. My son's having an extension done. When they were digging the footings, they found some unexpected drainage pipes. Thames Water came out and camera'd them, and found another waste pipe. Both were 3' feet down, and if I'd look for a place to put a rod, I'd hit both!

If this 18th proposal goes ahead, it might prove expensive.

With all little bit of planning it should be possible to arrange to use the reinforcing in the concrete as the earth electrode on new builds and extensions.
 
With all little bit of planning it should be possible to arrange to use the reinforcing in the concrete as the earth electrode on new builds and extensions.

I understand that's the provision. However, if the requirement for earth rod is applied to 132.16, and I'm putting an extra socket in an old terraced house in the town centre, it's going to be difficult and not cheap.
 
If I stand corrected I thought the draft said on the lines of preferably. I think that they will accept that when you go around to Mrs Muggins house to fit an extra socket it would not be practical to go and run earth cable outside to a earth electrode.
 
If I stand corrected I thought the draft said on the lines of preferably. I think that they will accept that when you go around to Mrs Muggins house to fit an extra socket it would not be practical to go and run earth cable outside to a earth electrode.

Reg 542.1.201 .........Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with 542.2.3 (which describes earth foundations).

Still not quite clear on this draft reg, perhaps I (and others have read it incorrectly?)
 
Back to my post.
Should of mention the service head is 2 separate connection blocks

And there is no earth coming off the neutral.

2 cables come in from the roof stright to the service connections
 

Reply to Earth arrangements confusion in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
275
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top