I was installing a smoke and heat alarm on an existing circuit today (aico ei141 )was already in place, so I have used the same type for the install.
All insulation and resistance tests were within limits.
I interlinked the alarms and all worked then rcd tripped. Initially we thought it was a faulty hoover as the householder had just plugged in a hoover.
I reset and the rcd on the other circuit tripped.
it can cause either rcd trips they only trip when the smoke alarms are pushed into positon. I rechecked all the cables again(visual /insulation/ resistance ) and it still trips as soon as a smoke alarm is connected.
The only thing I can think of was the loft was full of stuff and I had to move some out the way to get access. It may have disturbed another circuit although, nothing trips until the smoke alarm is put into place.
I appreciate this is a shot in the dark I am going back tomorrow and would appreciate any advice.
The smoke alarms are on battery backup so the client is covered.
I also tried connecting the smoke alarms on another circuit breaker in case that was faulty.
Its still tripping even on their own circuit?
I am new to inspection and testing and wondering if there is anything else to try before going through every other circuit.
thanks in advance..... I hate getting beat.
 
I was installing a smoke and heat alarm on an existing circuit today (aico ei141 )was already in place, so I have used the same type for the install.
All insulation and resistance tests were within limits.
I interlinked the alarms and all worked then rcd tripped. Initially we thought it was a faulty hoover as the householder had just plugged in a hoover.
I reset and the rcd on the other circuit tripped.
it can cause either rcd trips they only trip when the smoke alarms are pushed into positon. I rechecked all the cables again(visual /insulation/ resistance ) and it still trips as soon as a smoke alarm is connected.
The only thing I can think of was the loft was full of stuff and I had to move some out the way to get access. It may have disturbed another circuit although, nothing trips until the smoke alarm is put into place.
I appreciate this is a shot in the dark I am going back tomorrow and would appreciate any advice.
The smoke alarms are on battery backup so the client is covered.
I also tried connecting the smoke alarms on another circuit breaker in case that was faulty.
Its still tripping even on their own circuit?
I am new to inspection and testing and wondering if there is anything else to try before going through every other circuit.
thanks in advance..... I hate getting beat.
Borrowed Neutral may be??
 
Interesting fault ... if it's not a borrowed N and since these units are not earthed (iirc) how can they be tripping RCD? Cable fault right at connector perhaps? Especially if you've tried the unit on its own circuit and it still trips RCD. What happens if you plug the new alarm into the original position?
 
Am I correct in thinking there is an existing smoke detector circuit from which you have installed a further two detectors? If so where have you connected the new ones from.
 
Am I correct in thinking there is an existing smoke detector circuit from which you have installed a further two detectors? If so where have you connected the new ones from.
They are interlinked and I have visually checked them as well as muti meter test on that circuit.
basically live and neutral supply and then three core and earth between each alarm.
 
Interesting fault ... if it's not a borrowed N and since these units are not earthed (iirc) how can they be tripping RCD? Cable fault right at connector perhaps? Especially if you've tried the unit on its own circuit and it still trips RCD. What happens if you plug the new alarm into the original position?
I disconnected my additional circuit and reverted to the original and it is still tripping. I think I may have physically disturbed another circuit and created a fault, although I cant understand why its only when the smoke detectors are connected the rcd fault occurs .
 
Just a reminder on IR testing - Aico installation instructions specifically warn not to do it with units connected. Likewise accidentally making the interconnecting link wire live will trash them, if I recall correctly.
 
Just a reminder on IR testing - Aico installation instructions specifically warn not to do it with units connected. Likewise accidentally making the interconnecting link wire live will trash them, if I recall correctly.
I completed the ir testing with the cables unconnected from the smoke alarms. (the alarms were still in the box)Sad as it seems I actually tested each cable rather than link( R1-R2)as I had a new wander lead and it was a flat I was in.
 
So is the original circuit still in place and your new circuit is paralleled at the mcb?
Original cable which is direct from mcb was taken out from first smoke Alarm and is used as the live/ neutral /Earth supply in the loft void.
the interconnecting cables (three core and earth) for the alarms are linked in to this feed .
I will draw a diagram as I realise this explanation might not be clear

thanks for the help folks
 

Reply to rcd tripping after smoke alarm fitted. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top