Doomed

-
Arms
Joined
May 26, 2009
Messages
1,132
Reaction score
764
Location
Dorset
Doing some bits for an old boy and checked the bonding, the gas bond does not go back to the DB or MET, but is staked right next to the main earth rod.
I suppose it will effectively put the pipework in the same equipotential zone as the main earth, but just why make your life harder?
[ElectriciansForums.net] TT system and gas bond

[ElectriciansForums.net] TT system and gas bond
 
In effect the system now has 2 earthing conductors to 2 points of earth connection in parallel assuming the gas pipe has continuity to the met via the water pipe perhaps
Its not permitted for the service pipe to be used as the means of earthing
Thats what it will do if the resistance of its rod is lower than its mate nearby
 
In effect the system now has 2 earthing conductors to 2 points of earth connection in parallel assuming the gas pipe has continuity to the met via the water pipe perhaps
Its not permitted for the service pipe to be used as the means of earthing
Thats what it will do if the resistance of its rod is lower than its mate nearby
That's very true, but may also be the case in many TT systems where other services enter the building in metal pipework.
 
That's very true, but may also be the case in many TT systems where other services enter the building in metal pipework.

Very true Steve
The point I was trying to make was I believe the work shown is specifically prohibited by the regs
Its not a bonded service its a secondary earthing point
 
Doing some bits for an old boy and checked the bonding, the gas bond does not go back to the DB or MET, but is staked right next to the main earth rod.
I suppose it will effectively put the pipework in the same equipotential zone as the main earth, but just why make your life harder?
[ElectriciansForums.net] TT system and gas bond

View attachment 40331
why didn't they just put it onto the other rod ?
or, for the sake of equipotential difference......just call one Rodney and the other one Roderick........labelled up of course.
 
All around me is a zone of equipotential bonding, at least on Saturday nights :p
The book entitled - ‘The conquests of Wilko the Conqueror’, I had you pegged as married Wilko or is that what you are eluding to? Eeewh, with your wife? Disgusting !
 

Reply to TT system and gas bond in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
805

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top