Hi. Penny for a thought anyone. I'm still in holiday mode from yesterday...
Just been to a house after a plumber refused to touch the boiler (not before getting his £200 call out charge) saying there was an electrical fault and showing the customer his voltage pen light up on the water pipes & attic wooden joists saying there "was 20v" through them. The customer asked me to check it over before getting a plumber back.
Indeed on checking my 5V+ pen lit up on both pipes & joists and my voltage tester displayed voltage but of a negligable amount <12v.
The boiler is situated in a seperate part of the house with both water pipes and cables running through a narrow passage above a room joining the two main parts the house.
-TNCS system
- The voltage lowered on isolating the sockets & disapeared totally on isolating the lights. The cabling is messy and could be wrapped around the pipes in places (can't access to see full run).
My first suspicion was induced voltage from the close proximitary of the pipes and cables but that didn't ring right with the joists so I did some tests.
- Gas & water bonding is present.
- IR test on sockets >2Mohm
- IR test on lights 0.23 Mohm
The last time I came across continuity through walls it was a hidden nail in a skirting board catching the r1 to a socket so with the lights failing the IR test I'm thinking a nail etc could be the cause, but, When I reenergised the system less this failed lighting circuit I still have some voltage on the joists / pipes.
Now I'm thinking maybe it's both - induced voltage & a "nail"?
I've got to return to try and locate the light failings but wondered if anyone had any thoughts on the pipes/joists issue?
Just been to a house after a plumber refused to touch the boiler (not before getting his £200 call out charge) saying there was an electrical fault and showing the customer his voltage pen light up on the water pipes & attic wooden joists saying there "was 20v" through them. The customer asked me to check it over before getting a plumber back.
Indeed on checking my 5V+ pen lit up on both pipes & joists and my voltage tester displayed voltage but of a negligable amount <12v.
The boiler is situated in a seperate part of the house with both water pipes and cables running through a narrow passage above a room joining the two main parts the house.
-TNCS system
- The voltage lowered on isolating the sockets & disapeared totally on isolating the lights. The cabling is messy and could be wrapped around the pipes in places (can't access to see full run).
My first suspicion was induced voltage from the close proximitary of the pipes and cables but that didn't ring right with the joists so I did some tests.
- Gas & water bonding is present.
- IR test on sockets >2Mohm
- IR test on lights 0.23 Mohm
The last time I came across continuity through walls it was a hidden nail in a skirting board catching the r1 to a socket so with the lights failing the IR test I'm thinking a nail etc could be the cause, but, When I reenergised the system less this failed lighting circuit I still have some voltage on the joists / pipes.
Now I'm thinking maybe it's both - induced voltage & a "nail"?
I've got to return to try and locate the light failings but wondered if anyone had any thoughts on the pipes/joists issue?