I bought a Nest and think i know how to fit it but want to check. I have a Glow Worm 30CXI combi boiler so only need to connect the heating side of things up and not the water.

I have located a pink and a light blue wire which appears to then connect to the wire which then links to the thermostat in another room. Is it a case of connecting the light blue and pink wires to numbers 2 & 3 on the nest heat link (and obviously rewire the thermostat to T1 & T2)? Does it matter which colour goes into 2 or 3?
 
That all depends on what the pink and blue wires are connected to and what they do?
It’s very unusual to see pink and light blue wires in an installation though, you haven’t opened up the boiler and started messing with the internal wiring have you?
 
I have located a pink and a light blue wire which appears to then connect to the wire which then links to the thermostat in another room. Is it a case of connecting the light blue and pink wires to numbers 2 & 3 on the nest heat link (and obviously rewire the thermostat to T1 & T2)? Does it matter which colour goes into 2 or 3?
in you past life ,did you work for the bomb disposal ?
 
Sorry if i'm hijacking this a thread a bit but I have said I will install a Nest thermostat for someone.
I have done many wireless stats a few Salus it500 and one Hive before.
The stats were all battery powered apart from the Hive that had to be plugged into a usb if i remember correctly although this was a couple of years ago and may have changed now.
From my understanding the Nest needs a 12v supply and ideally they want it were the old stat is so can you just put a pair from the three core in T1 and T2 on the heatlink for this and is 1.5mm a nightmare to fit in the stat terminals?
 

Reply to Nest on a Glow Worm 30CXI Combi Boiler fitting in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
502
D
  • Article
Issues With Nest Generation 3 Operating Boiler? I have a Google Nest Generation 3 Thermostat/Heatlink, Thermostat is in the hallway and operates...
Replies
0
Views
76
Dulbert
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top