Hello.

I'm new here so my apologies if this post ended up in the wrong forum.

I have a basic understanding of phases and voltage and the lot. Today I'm trying to wrap my head around how I might be able to split one 3-phase 240v 50a source to accommodate 3 high draw theater fixtures.

Here's what I know about each of the 3 fixtures that may be useful:
-Rated at 1700VA.
-Accepts a 240v 15a plug (twist-lock, HOT, HOT, GND.)
-1200w bulb.
-Amperage test shows 12a across both phases.
-The furthest fixture from the source would be 70' one way.

My question is how to power all 3 of these fixtures of of the 240v 50a source? If so, how would you do it safely?

Thank you for your help.
 
Would I be correct in thinking you're in America?

As I understand it you deal with multi phase differently over there - you would probably wire these lights the same way as you would a tumble dryer or air conditioner.

Ordinarily theatrical lights would be dimmed, so you'd need a suitable dimmer. This might even 'split' your supply for you - probably something a bit like this: http://www.theatrecrafts.com/archive/documents/act3datasheet.pdf
 
Again not totally conversant with US 3 phase but in theory connecting them equally between phases should ensure similar loading on each cable.
So light 1 on A and B phase, light 2 on B and C phase, light 3 on A and C phase.
It would also be useful to know if there were other loads on this supply so that you can accommodate these in the calculations.
 
Would I be correct in thinking you're in America?

As I understand it you deal with multi phase differently over there - you would probably wire these lights the same way as you would a tumble dryer or air conditioner.

Ordinarily theatrical lights would be dimmed, so you'd need a suitable dimmer. This might even 'split' your supply for you - probably something a bit like this: http://www.theatrecrafts.com/archive/documents/act3datasheet.pdf

I made a mistake when I said 3-phase. What I meant was 2-phase (American) along with a neutral (that is ommited) and ground obviously.

Luckily these fixtures are locally dimmed so there is no need for a dimming power supply.

Thank you for your suggestion.

Again not totally conversant with US 3 phase but in theory connecting them equally between phases should ensure similar loading on each cable.
So light 1 on A and B phase, light 2 on B and C phase, light 3 on A and C phase.
It would also be useful to know if there were other loads on this supply so that you can accommodate these in the calculations.

Luckily these 3 fixtures will be the only devices on this supply.

Thank you for your help.
 
Hello.

I'm new here so my apologies if this post ended up in the wrong forum.

I have a basic understanding of phases and voltage and the lot. Today I'm trying to wrap my head around how I might be able to split one 3-phase 240v 50a source to accommodate 3 high draw theater fixtures.

Here's what I know about each of the 3 fixtures that may be useful:
-Rated at 1700VA.
-Accepts a 240v 15a plug (twist-lock, HOT, HOT, GND.)
-1200w bulb.
-Amperage test shows 12a across both phases.
-The furthest fixture from the source would be 70' one way.

My question is how to power all 3 of these fixtures of of the 240v 50a source? If so, how would you do it safely?

Thank you for your help.

EDIT: 2-Phase not 3-Phase.
 
Hi @Marshall Kidd, welcome to the forum.

Can we establish firstly and given your age here, if this is theory or practical advice you are requesting?
I cannot personally comment on USA regulations or practices as we are a UK regulation based forum and your reg's are not my area of expertise, someone of your age (17) should not be undertaking any work like this unsupervised by a competent person, I would suggest you ask them your query on this matter as they will be familiar with both your regulations and the install itself.
If this is theory or coursework then we advice you seek such advise off your tutor as we do not give coursework answers out all though we are willing to nudge you in the correct direction if you can show your calculations and/or understanding on the matter.
 
In the UK we wouldn't have an issue with wiring multiple 230v sockets onto the same circuit, however those big plugs we use which other countries laugh at are individually fused, so whatever the circuit is rated at (usually 20A or 32A) the most you can continuously draw is 13A.
In this instance if you've got enough space in the distribution board (panel) I'd probably wire them as 3 separate circuits, protected by an MCB appropriate to the size of the cable (probably 10A or thereabouts).

This said it would need to be done in accordance with NEC which I know nothing about, and may need to be done by a state registered electrician.
 
In the UK we wouldn't have an issue with wiring multiple 230v sockets onto the same circuit, however those big plugs we use which other countries laugh at are individually fused, so whatever the circuit is rated at (usually 20A or 32A) the most you can continuously draw is 13A.
In this instance if you've got enough space in the distribution board (panel) I'd probably wire them as 3 separate circuits, protected by an MCB appropriate to the size of the cable (probably 10A or thereabouts).

This said it would need to be done in accordance with NEC which I know nothing about, and may need to be done by a state registered electrician.

Thank you for your reply.

Unfortunately we cannot spare any room in this current fuse box due to some poor management (ugh) and the next closest one is about 100ft away. This one circuit is all that we have to work with.

If I understand what your saying correctly, would running a 50a circuit to a smaller box (closer to the fixtures) with 3 individual 240v 15a breakers (one for each fixture) make sense?

Thanks.
 
Hi @Marshall Kidd, welcome to the forum.

Can we establish firstly and given your age here, if this is theory or practical advice you are requesting?
I cannot personally comment on USA regulations or practices as we are a UK regulation based forum and your reg's are not my area of expertise, someone of your age (17) should not be undertaking any work like this unsupervised by a competent person, I would suggest you ask them your query on this matter as they will be familiar with both your regulations and the install itself.
If this is theory or coursework then we advice you seek such advise off your tutor as we do not give coursework answers out all though we are willing to nudge you in the correct direction if you can show your calculations and/or understanding on the matter.

Hello. Apologies for not clarifying this earlier.

I will not be the one installing or organizing any of this. The risk is not worth it.

What I am trying to do is get in touch with the buildings (qualified) electrician to sort out when he would be able to put this system in.

I'd figured I'd come here and ask some experts to get a better idea of what we would like done exactly.

Thank you for your concern.
 
I think from a UK perspective there are the two methods indicated by AdamW. I believe loads are generally more separated in the US than the UK, so would tend toward the three circuits approach.
However it would be important to check your local codes to ensure you are complying with them.
[ElectriciansForums.net] Splitting 3-phase circuits for 3 high draw theater fixtures.
 
I think from a UK perspective there are the two methods indicated by AdamW. I believe loads are generally more separated in the US than the UK, so would tend toward the three circuits approach.
However it would be important to check your local codes to ensure you are complying with them.
View attachment 41667

Thank you for the advice. I will bring it up with the electrician installing the circuit(s.)

Is there a benefit in one over the other?
 

Reply to Splitting 3-phase circuits for 3 high draw theater fixtures. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

  • Question
Here's how we generally protect circuits in the States, although GFCI breakers are also available.
Replies
9
Views
2K
  • Question
How did it go?
Replies
12
Views