I am certainly not an expert, just generally able to apply the requirements of the regs.
To expand on Strimas post, if you have an evenly distributed load on a long lighting circuit, say 100W every 20m then on average you can use the formula you describe as the volt drop will be high because all lights are taking current at the start of the circuit and drop down as you get to the end where only one light is taking current but it will also rise at the end because of the length of circuit, so on average your volt drop would be that for when the load is only half the total design current.
Not an equation I would usually use as you normally need to know the maximum volt drop. but for a rough estimate and a likely successful outcome it would work.
Additionally it is possible on long radial circuits to have a large csa at the start where the load current is high, so as to reduce volt drop and reduce the csa as you get further out and the load current, and so volt drop, is lower, in this case it may be necessary to know the fault current at the points where the csa changes in case the cable does not have the energy withstand of the fault current at origin.
I cannot see why you would ever need to know fault current at the end of the circuit though.
I attach a diagram from a previous post about calculating volt drop that is not totally in line with this post but may help explain the idea.

To expand on Strimas post, if you have an evenly distributed load on a long lighting circuit, say 100W every 20m then on average you can use the formula you describe as the volt drop will be high because all lights are taking current at the start of the circuit and drop down as you get to the end where only one light is taking current but it will also rise at the end because of the length of circuit, so on average your volt drop would be that for when the load is only half the total design current.
Not an equation I would usually use as you normally need to know the maximum volt drop. but for a rough estimate and a likely successful outcome it would work.
Additionally it is possible on long radial circuits to have a large csa at the start where the load current is high, so as to reduce volt drop and reduce the csa as you get further out and the load current, and so volt drop, is lower, in this case it may be necessary to know the fault current at the points where the csa changes in case the cable does not have the energy withstand of the fault current at origin.
I cannot see why you would ever need to know fault current at the end of the circuit though.
I attach a diagram from a previous post about calculating volt drop that is not totally in line with this post but may help explain the idea.