Hi, I’ve been asked to install lighting and 3 sockets (one of which is for a fridge) in a wooden shed. Due to location of consumer unit the only feesable option is to use the feed from the Jacuzzi which is on the non RCD side of the CU using a 40A MCB with 10mm Twin & Earth cable and own isolator switch.

Total length of cable would be 25 meter’s, 19m indoors and 6m outdoors leading to the shed (not buried) to mini CU with RCD protection

The jacuzzi is 6Kw and fridge 2Kw so 40A mcb will handle load and should be most used at anyone time.

My question is, if I extend the 10mm t & e that inside the house with 6m of 10mm SWA outside the house does it alter my cable calculations as they have different reference methods?
 
looking at the build, which is relatively new, the size of cable and the worst case scenario of the Jacuzzi enclosed in conduit in thermally insulated walls as other methods e.g. show a 6mm cable size is suitable
The SWA will have to be clipped to or under decking which is above ground by a couple of foot
 
A 6mm cable might be suitable for the load but im pretty sure it wont wont the current carrying capacity for a 40A mcb once derating factors have been taken into account. Also i was always under the impression that a jacuzzi needed rcd protection as most manufactures recommend als if you are putting sockets for genaral use in the shed these will also need to be rcd protected.
 
it's round the back that 'er indoors likes to chill.

[ElectriciansForums.net] Shed and jacuzzi advice
 

Reply to Shed and jacuzzi advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
641
  • Question
The original post could be clearer, but I believe you're essentially asking if the use of a lower rated rcbo would prevent tripping of an upstream...
Replies
5
Views
2K
nicebutdim
N
  • Question
Why aren't you asking them?
Replies
5
Views
783
  • Question
I think the original was 'no lyrics'
2
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks