No power to the house, didn't take long to find the problem.

[ElectriciansForums.net] An interesting callout yesterday....

[ElectriciansForums.net] An interesting callout yesterday....
 
If you know what you're doing, unless the cables have to follow an very unfavourable route, you can arrange for zero stress on the terminations. They should be pre-formed into shape so that they sit comfortably in position before tightening the screw, without pressing forcibly together or onto any parts of the switchgear or enclosure. Lots of installers don't take the time to do this and rely on the terminals to hold cables that are too short, too long, too tangled or just wrongly dressed into position.

Then we come to the issue of the torque screwdriver...
 
Apart from poor workmanship its high time manufacturers put two screws back onto these sort of terminations. The actual length of conductor that enters these connections is pitiful. You'd only need to fart on one to shift it once tightened.

Friday I fitted one of the newest Wylex boards, they now have double depth tail terminals with 2 screws on each, I filled it with their new mcb sized double pole rcbos aswell,,,, bloody lovely board :) I shall be using them from here on out
 
I have just turned up this reference for a trial done on meter tail terminations by the Electricity Safety Council:

https://www.----------------------------/mediafile/100013801/Meter-Tail-Investigation-Report.pdf

For the busy reader the conclusions, observations and recommendations are on page 10/10.
 
I have just turned up this reference for a trial done on meter tail terminations by the Electricity Safety Council:

https://www.----------------------------/mediafile/100013801/Meter-Tail-Investigation-Report.pdf

For the busy reader the conclusions, observations and recommendations are on page 10/10.
Meter changes will be an issue on a lot of installations, however in wasn't it the callout fault on this job. The tails come from Consumer Unit into Isco's/Henley blocks. It was down to poor workmanship from the electrician that did the work. The rest of the installation is a mess as well:(
 
On many many wylex boards that I have stripped out, there has been not so tight terminations on quite a few, but have rarely witnessed damage to conductors by arcing. Give me dual screw terminations any day.
With new consumers units, I do find that a proper tails gland helps a lot and holds tails in place very well. Uninsulated cord end ferrules are probably the best solution to rectifying poorly designed terminations.
 
I ordered some 35mm tails for a job last year, the brown had less strands than the two - dufferent brand... But god was the blue so much nicer to work with and better in the terminal so i agree with that report.. Dont know if we can specifically order it that way though?
 
I ordered some 35mm tails for a job last year, the brown had less strands than the two - dufferent brand... But god was the blue so much nicer to work with and better in the terminal so i agree with that report.. Dont know if we can specifically order it that way though?
 

Reply to An interesting callout yesterday.... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would have to agree with @James to hire an electrician to measure the voltage coming in to the panel. If you have 240vac phase to phase then you...
Replies
3
Views
1K
Yes I think back in the dark old days they were called deeds but are now called contracts and some still refer to it as deeds like I did! Sounds...
Replies
4
Views
239

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top