Hi all.
Don't have much experience on this topic.

Called to a job with an electric boiler. It has a dedicated 10mm supply from a 50A MCB. I narrowed down the fault the the contactor which was only feedig 1 of tge 3 elements and had scorching marks around the other 2 terminals. And is currently a 20A. The boiler has 3 x 3kw elements.
My query is surely the 20A is insufficient for the 9kw load from the elements and shouldn't I fit a 40A contactor in it's place.

Thanks
 
Firstly is this 1ph or 3ph and if the latter is this 9Kw per phase or 3Kw a phase would be my first few questions, have you clamped the load to see what 1 element pulls if you are in doubt?
I guess 1ph but that would rely on the fact the installer got it right and we should never assume in this game.
 
Your contactor is 20amp per pole so it is sufficient for a resistive load a 3kw element per pole, the problem is likely to be poor termination, this is a high current load, have the cable ends been suitable dressed with rated crimps or lugs?
What is the brand of contactor - is it a recognised reliable brand or cheap import.
 
Firstly is this 1ph or 3ph and if the latter is this 9Kw per phase or 3Kw a phase would be my first few questions, have you clamped the load to see what 1 element pulls if you are in doubt?
I guess 1ph but that would rely on the fact the installer got it right and we should never assume in this game.
There is usually an electronic control board which is installed with his system but it's blew in the past and someone has hard wired it up with this 20A contactor and a 16A timer
 
Your contactor is 20amp per pole so it is sufficient for a resistive load a 3kw element per pole, the problem is likely to be poor termination, this is a high current load, have the cable ends been suitable dressed with rated crimps or lugs?
What is the brand of contactor - is it a recognised reliable brand or cheap import.
I've attached a photo of the contactor which is a Chint NC1-0910

[ElectriciansForums.net] What contactor size for a 9kw electric boiler
 
No I would never install this.
The black box/housing above the contactor usually would contain the main pc control board with digital display. Someone just removed that and fitted.this instead
if i was you i wouldnt try and improve upon this install without starting from fresh

id say the "fault" is down to poor installation than the boiler or contactors themselves
 

Reply to What contactor size for a 9kw electric boiler in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Leicestershire

Thread Information

Title
What contactor size for a 9kw electric boiler
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top