Hi all.
Don't have much experience on this topic.

Called to a job with an electric boiler. It has a dedicated 10mm supply from a 50A MCB. I narrowed down the fault the the contactor which was only feedig 1 of tge 3 elements and had scorching marks around the other 2 terminals. And is currently a 20A. The boiler has 3 x 3kw elements.
My query is surely the 20A is insufficient for the 9kw load from the elements and shouldn't I fit a 40A contactor in it's place.

Thanks
 
I agree. It's a joke that people still complete works like this and leave and even get paid for it.
best thing to do now is go and show the customer the state of the electrical installation

a contactor may not be heavy in your hand, but on the end of a cable vibrations can cause movement, which causes arcing , everytime that contactor comes on its going to move the connections, loosening them slightly

i think you will find once you clean up this mess and install properly there will be no more "faults" with the system
 
I take it elsparko you don't fit many contactors, I would never choose that brand to run a heating load or anything tbh, they are cheap for many reasons, I have come across loads of them failing and been the cause of problems.
7.5Kw budget chint contactor about £10
7.5Kw recognised quality brands £40 - £90

You get what you pay for and the elements may have gone due to age but if there is overheating at the terminals of this contactor then I wouldn't overlook it is the contactor as the cause here of the cables getting hot.
 
I take it elsparko you don't fit many contactors, I would never choose that brand to run a heating load or anything tbh, they are cheap for many reasons, I have come across loads of them failing and been the cause of problems.
7.5Kw budget chint contactor about £10
7.5Kw recognised quality brands £40 - £90

You get what you pay for and the elements may have gone due to age but if there is overheating at the terminals of this contactor then I wouldn't overlook it is the contactor as the cause here of the cables getting hot.
i may not do many of them but i know that chint is a brand only seen to be used by diyers , ive always believed in buy cheap buy twice

i still think the install is questionable lol
 
i may not do many of them but i know that chint is a brand only seen to be used by diyers , ive always believed in buy cheap buy twice

i still think the install is questionable lol

Hence I said upgrade it, if the OP repairs it then he becomes responsible for it and that includes the mess it is in, best to strip it out dinrail mount a quality contactor with dinrail connectors and linking clips for them, I would even provide a derated fuse size for the elements unless he can show the Zs is good at the elements.
 
my contactor experience mainly comes from lighting controls, but the theory remains the same

a contactor just held in place by the cables it supplies which are not themselves secured could lead to loose connections, but like you say chint is a pile of crap so could just as easily be the contactor itself, i wouldnt fit a new contactor without sorting out the mess though
 
I wasn't arguing your theory elsparko and it is quite possible for the reasons you raise, I was just saying that the install (viewable in the upload) should be scrapped and started again but of course the customer will be given the option he does this or walks... I meant the whole mess too in the picture not just the contactor which I explained earlier.
 
I've contacted the agent in the meantime and spelled out the issues. I agree rather chop it all out and start again with the components designed for the system I.e a new main control board and capillary thermostat to start with.
 
Looked up that contactor - advertised as 9A rated - so not tooo good for 3kW loads :eek:

[ElectriciansForums.net] What contactor size for a 9kw electric boiler
 
Last edited:
Hi all.
Don't have much experience on this topic.

Called to a job with an electric boiler. It has a dedicated 10mm supply from a 50A MCB. I narrowed down the fault the the contactor which was only feedig 1 of tge 3 elements and had scorching marks around the other 2 terminals. And is currently a 20A. The boiler has 3 x 3kw elements.
My query is surely the 20A is insufficient for the 9kw load from the elements and shouldn't I fit a 40A contactor in it's place.

Thanks
 
Oops - just read the rest of the advert, that's the AC3 rating that's 9A. The AC1 is quoted as 20A, but they don't say how many operations it's good for :)
 
Last edited:

Reply to What contactor size for a 9kw electric boiler in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Leicestershire

Thread Information

Title
What contactor size for a 9kw electric boiler
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--