Hi guys some help required!! My sister runs a centre and has bought 5 x 3kw table top combined oven and hobs they are supplied with plugs which cant be removed as that will invalidate the warrentys. There are 3 spare slots on the consumer unit how can she safely run all 5 appliances. she says when in use the oven and hobs will be in use so will be running at full pelt. She had a spark in who suggested running 3 4mm circuits to serve the appliances. But just by browsing these forums and looking what you guys say I'm a little worried. Someone mentioned anything 3kw or above should have it's own circuit??
 
Hi guys some help required!! My sister runs a centre and has bought 5 x 3kw table top combined oven and hobs they are supplied with plugs which cant be removed as that will invalidate the warrentys. There are 3 spare slots on the consumer unit how can she safely run all 5 appliances. she says when in use the oven and hobs will be in use so will be running at full pelt. She had a spark in who suggested running 3 4mm circuits to serve the appliances. But just by browsing these forums and looking what you guys say I'm a little worried. Someone mentioned anything 3kw or above should have it's own circuit??

But this is what has been suggested no ? Separate circuit for each appliance ?
 
nothing to stop an electrician putting 2 of these appliances on a 32A or a 40A circuit run in 6.0mm cable. as they are fixed loads. overload protection is by the BS1362'sin the plug tops.diversity will also apply.
 
Well OP said 6 in his title and 5 in his question. Then when on to make things clear as mud. A picture or link would have helped. What do the manufacturers instructions say?

[ElectriciansForums.net] 6 3kw table top ovens and hobs
 

Reply to 6 3kw table top ovens and hobs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Personally I'd always fit 6mm. There was a thread on here a month or two ago where an electrician had run 4mm on a 32A breaker, another...
Replies
6
Views
3K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K
  • Question
Indeed. The cordless one we bought last year is one of the best things we have ever bought.
2
Replies
28
Views
4K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
Lots of vibration is good for loosening any terminals or fixings so it could be something quite simple when investigated
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks