Could any of you help me out with this one please as I don't usually do apartment blocks and haven't come across this scenario before.
Large apartment block built 2004. Looks like the tails enter the consumer unit via Armoured cabling with the armour being used as the main earth & bolted to the top of the metallic CCU (can't confirm as the CCU is up to the ceiling). PSCC = 0.56ka. The linking cable from the SWA bolt to the earthing bar is 4mm2. Now (not taking the earth bar securing/earthing screw to CCU into account) my calculations suggest the size is adequate. But with the tails looking like 10mm (hard to tell as they are is soft flimsy sheaving) my understanding is that 4mm linking cable should be at least 10mm2 to meet the regs.
Anyone tell me if I'm wrong or, as I'm never wrong! ;-) what code it would be. I'm thinking C2?
Cheers,
Could any of you help me out with this one please as I don't usually do apartment blocks and haven't come across this scenario before.
Large apartment block built 2004. Looks like the tails enter the consumer unit via Armoured cabling with the armour being used as the main earth & bolted to the top of the metallic CCU (can't confirm as the CCU is up to the ceiling). PSCC = 0.56ka. The linking cable from the SWA bolt to the earthing bar is 4mm2. Now (not taking the earth bar securing/earthing screw to CCU into account) my calculations suggest the size is adequate. But with the tails looking like 10mm (hard to tell as they are is soft flimsy sheaving) my understanding is that 4mm linking cable should be at least 10mm2 to meet the regs.