Eggsactly. Yet people on here still argue that its needed cos some leaflet translated from a far east countries language says so.but a 3A fuse would have prevented that....... NOT.
Agreed but when you can get an extractor for two bob and three Woodbines it is not going to happen.An appropriately sized fuse designed for use in appliances and built in to the fan would stand a far better chance of preventing fire than a 3A plug fuse
Fear not, the new arc detection devices will come to the rescue in the near future.....ALSO NOT.but a 3A fuse would have prevented that....... NOT.
but a 3A fuse would have prevented that....... NOT.
What you mean maybe they should start producing decent products again?Fear not, the new arc detection devices will come to the rescue in the near future.....ALSO NOT.
Interesting, do you think ZP is considered with the construction of a chuck away extract fan.This is what happens when an 'impedance protected' shaded pole motor is pad mounted in a cheap plastic frame and it suffers a locked rotor condition. The jammed blade means there's no air over the motor to cool it plus the higher LRA means more heat as well. The plastic mounts weren't capable of handling the heat. Not sure it was actually a fire risk because I doubt it would have reached flash point temperature but certainly poorly constructed and designed.