My system has had an intermittent problem for the last few months. The inverter has occasionally been reporting PV Voltage Too High, then it would recover after a few minutes. It also didn't do it every day.
Now In the last few days it has started to do it more frequently and it appears to give up after retrying even when the voltage drops and it stays locked-out for the rest of the day. It seems to be set to fault at >507V but is often now logging up to 599V which seems to be its max.
Looking back at the logs I can see that in summer for the preceding 3 years the max DC voltage recorded was never >252V during June/July. I can also now see from the history that it started to creep up around last autumn 2017, peaking at over 300V some days.
Since this March I've also been getting an occasional "PV Insulation Fault" up until the last few days that was only for a few minutes in the morning when the system first started and then it went away - I put that down to some minor moisture ingress somewhere that quickly dried out as the sun came up. However, this earth fault issue seems to have become semi-permanent in the last couple of days with the system seeming to stop retrying until powered off for an hour or two.
Can anyone suggest why the panels would now appear to be outputting a much higher DC voltage than they're rated for?
There is another thread with a possibly similar issue that suggested theirs may be an inverter fault.
As with many installers who were active in the UK PV book, my installer from 2011 is no longer trading, although I've contacted him and he may hopefully come and do some basic checks. The re-branded Powercom/pcm-ups/SolarKing inverter is also out of warranty, so that's a dead end if it is the inverter.
I guess if it is an inverter fault and anyone has any experience of this being a common issue (e.g. "it's a classic symptom of --- component failure") then I could replace something - I replaced failed grid relays myself a couple of years ago. I know that capacitors do fail on far more devices than people realise but I thought the big "capacitor plague" issue ended around 2007 when all the cheap manufacturers changed materials and my inverter would presumably have been made well after that.
Any advice/ideas/suggestions welcome. At the weekend I'll begin some more in-depth diagnosis, carefully measuring each string's voltage, etc, to see if they match what the inverter is reporting.
Now In the last few days it has started to do it more frequently and it appears to give up after retrying even when the voltage drops and it stays locked-out for the rest of the day. It seems to be set to fault at >507V but is often now logging up to 599V which seems to be its max.
Looking back at the logs I can see that in summer for the preceding 3 years the max DC voltage recorded was never >252V during June/July. I can also now see from the history that it started to creep up around last autumn 2017, peaking at over 300V some days.
Since this March I've also been getting an occasional "PV Insulation Fault" up until the last few days that was only for a few minutes in the morning when the system first started and then it went away - I put that down to some minor moisture ingress somewhere that quickly dried out as the sun came up. However, this earth fault issue seems to have become semi-permanent in the last couple of days with the system seeming to stop retrying until powered off for an hour or two.
Can anyone suggest why the panels would now appear to be outputting a much higher DC voltage than they're rated for?
There is another thread with a possibly similar issue that suggested theirs may be an inverter fault.
As with many installers who were active in the UK PV book, my installer from 2011 is no longer trading, although I've contacted him and he may hopefully come and do some basic checks. The re-branded Powercom/pcm-ups/SolarKing inverter is also out of warranty, so that's a dead end if it is the inverter.
I guess if it is an inverter fault and anyone has any experience of this being a common issue (e.g. "it's a classic symptom of --- component failure") then I could replace something - I replaced failed grid relays myself a couple of years ago. I know that capacitors do fail on far more devices than people realise but I thought the big "capacitor plague" issue ended around 2007 when all the cheap manufacturers changed materials and my inverter would presumably have been made well after that.
Any advice/ideas/suggestions welcome. At the weekend I'll begin some more in-depth diagnosis, carefully measuring each string's voltage, etc, to see if they match what the inverter is reporting.